Jennie1220
- Tappahannock VA
- electrician
There is no necessity for a flexible connection for that type of equipment.(2) Flexible Connections.
Where necessary to employ flexible connections, as at motor terminals, one of the following shall be permitted: ...
The light fixture is mounted on an adjustable bracket so I hoping that would be seen as a necessity for that flexible connection.Just having splices does not trigger a requirement that the enclosure have seals. However, I highly doubt that I would approve the cord connection for that fixture as I do not see the installation being permitted in 501.10(A)(2).
And because of the low ceiling we could not mount them on the ceilingThe light fixture is mounted on an adjustable bracket so I hoping that would be seen as a necessity for that flexible connection.
This picture show how the light was originally mounted but the light would have been shining right in your face so I elected to use an adjustable mount with the flexible connection.
Will do.. Thanks for the help!I would have to see the actual installation, but might require a flexible coupling in place of the flexible cord. But also might accept the cord. You need to run this by your AHJ.