I know we've discussed this before but it a bit fuzzy and I want to be clear.
1. Class 2 wiring can't be run with power(600v) conductors. The only way to do this is re-classified them as class 1 and that entails removing all class 2 marking from power supplies etc.?
2. Class 2 wiring can be run exposed(not enclosed in conduit) above hung ceilings?
3. Class 2 wiring is rated for 150v?
Interesting that this MC-PCS cable is allowed for class 1 and class 2 wiring method. I mentioned this a while ago but can't locate the post.
https://www.southwire.com/products/35959.htm
1. Class 2 wiring can't be run with power(600v) conductors. The only way to do this is re-classified them as class 1 and that entails removing all class 2 marking from power supplies etc.?
2. Class 2 wiring can be run exposed(not enclosed in conduit) above hung ceilings?
3. Class 2 wiring is rated for 150v?
Interesting that this MC-PCS cable is allowed for class 1 and class 2 wiring method. I mentioned this a while ago but can't locate the post.
https://www.southwire.com/products/35959.htm