Nothing directly addresses this in the NEC, it is all about listing and instructions that are a part of the listing. 110.3(B) says you need to follow instructions included in the listing.Looking for a NEC reference concerning the use of substitute or classified circuit breakers in panelboards. Thanks
many do. If it is "classified" it can be used in whatever loadcenters it is classified for.So...... do inspectors enforce this?
I know, same goes for any kind of retrofit item though. Some popular applications these days is LED trims being installed in recessed lighting cans, or LED tubes being installed in luminaires originally designed for specific fluorescent lamps.UL states we must follow the directions included with the equipment.
Siemens instructions say use only Siemens Type "X" breakers.
GE instructions say use only GE Type "X" breakers.
Eaton states we can use their clasified breakers in GE and Siemens panels.
Using classified breakers contradicts what UL states we are supposed to do. Who's instructions are we supposed to follow?
Unless I misunderstand something, why would Eaton make a "classified breaker" for one of their own product lines?I use CL breakers in all panels up to and including 50A except CH panels, because Eaton didn't get them listed for those panels. Go figure
I love CL because I don't have to stock every brand under 60A, except Eaton's BR and Sq D's QO.
It would seem Ohm's remark was some kind of unsolicited advertising without a clue.Unless I misunderstand something, why would Eaton make a "classified breaker" for one of their own product lines?