In the interest of full disclosure, I don't have access to the latest API RP-500. But the 2002 edition doesn't consider the area inside the dike Division 1. See Figure 7.
I know what is done and that it is typically safely done, and I work in a plastics manufacturing plant every day, but the plant has very few Division 1 areas.Don -
I think you are stuck in fire-fighter mode. And I highly suspect you don't do work in these areas.
My first questions are:
Q1: What danger of fire?
Q2: What danger of inhalation hazard?
The area is sniffed clear and monitored - remember?
Here is an example: Cutting and welding inside of a tank yard - products with a flashpoint less than 100F. Yes, people actually do this stuff. I picked this one because it's somethng I did in a previous life - so it is not contrived.
Inside the tankyard, below the berm is DIV 1 - as I recall (API RP 500) Now, how do you suspose that one does this with a 1,000,000 gallons of Av-gas or Jet-B staring at you over your shoulder. The ppe consists of treated cotton fire resistant coveralls. Nomex gets ate up from the welding splatter - its useless. There are no escape bottles, or in-use SCBA - that's riduculus. Provided you bothered to read my posts, you already know how one does this safely - with a couple of extras:
Isolate and clean up the piping.
No tank loading while work is on-going - don't want any venting
Post a fire watch - with an extinguisher or two, and a shovel
Now that you are working up a good case of indignant righteousness - I have a couple of questions:
Q3: This ppe that you insist is needed for work in a C1D1 area (non-confined space), just what standard are you using to select the protection level?
Q4: Once a day the company sends the yardman to record the mechanical level gauges. Do you expect her to wear the same gear as the welded plumbers?
ice
The classification tells me that we can be at or above LEL under normal operating conditions.Don -
...
Q1: What danger of fire?
See previous answer.Q2: What danger of inhalation hazard?
What level do you activate your flammable gas alarm at? Many set the meter alarm at 10% of LEL, but for a number of products you are already above IDLH at 10% of LEL.The area is sniffed clear and monitored - remember?
Yes I am aware that is a common practice and that there is no practical way to avoid doing that, but if it is really a division 1 area, I don't think that type of work should be permitted.Here is an example: Cutting and welding inside of a tank yard - products with a flashpoint less than 100F. Yes, people actually do this stuff. I picked this one because it's something I did in a previous life - so it is not contrived.
It would have to be based on what protection is required for the product at a concentration at or above...Q3: This ppe that you insist is needed for work in a C1D1 area (non-confined space), just what standard are you using to select the protection level?
Other than the PPE that is specific for the welding task, yes the same level of PPE is required.Q4: Once a day the company sends the yardman to record the mechanical level gauges. Do you expect her to wear the same gear as the welded plumbers?
I see a disconnect between our two viewpoints.Yes I am aware that is a common practice and that there is no practical way to avoid doing that, but if it is really a division 1 area, I don't think that type of work should be permitted. ....
I would agree...having an escape bottle would not be good enough...in my opinion, if you are in a Class I Division 1 area you need to be using PPE suitable for the hazard...not just have it available. In the case of flammable products that may also require PPE to protect you from fire as well as inhalation hazards.
To me Division 1 means the flammable concentration can exist under normal operating conditions. Yes a lot of the time it is clear, but how fast can it change, how fast does the meter react, how fast can you run?When I say "Div 1", I mean, "a significant concentration of flammable vapor exists more often than 1 hour in 8000 hours" That leaves a lot of time the area is clear. One drains, isolates, cleans, ventilates. And since one might choose to not have all the equipment in the area locked out, post a fire watch and gas monitor. ...
I know that where I am at the combusible gas detectors are not gas specific and that they alarm at 10% of LEL, but I also know that for many of the products here 10% of LEL is way above IDLH. They are calibrated for either propane or pentane, not sure which one, and those are not the flammable products that are used here. In there defense any hot work is shut down if there is any reading on the combustible gas detector, but you don't know that there is a reading unless you are looking at the display. The Division 1 areas are very limited at this plant and so it would be rare to be in such an area.Concerning gas detectors: One uses the type required for the job conditions. One gets the equipment required for the job. No different than any other vocation. Can they be hard to use or complicated? (complicated defined for this purpose as, "more than one button") Can be. So what? Welded plumbing in classified areas is specialized work. Electrical maintenance is classified areas is specialized work. One doesn't send out shoe clerks - one sends out trained techs.
That is a good point. I forgot about the actual fire issue and was just thinking about the respiratory issue. I guess, I have to say that you cannot enter a Division 1 area. The only document is the definition of Division 1 and it says that a flammable concentration may exist under normal operating conditions. Based on that I don't see how an employeer can send an employee into the Division 1 area.I'm stuck - I'm still asking: I know how to pick out ppe for arc-flash. I can pick out respiratory protection for hazardous atmospheres. So how do I pick out ppe clothing to walk through a Div 1 area like a pumphouse that won't have a hazardous atmosphere unless there is a seal leak? What document or standard do you reference?
ice
...
When I say "Div 1", I mean, "a significant concentration of flammable vapor exists more often than 1 hour in 8000 hours" That leaves a lot of time the area is clear. One drains, isolates, cleans, ventilates. And since one might choose to not have all the equipment in the area locked out, post a fire watch and gas monitor.
rbalex - I did not look up the number of hours to diferentiate between D1 and D2. Please correct if available.
?
Okay, I pulled my copy of API RP 500, 3rd edition, Dec 2012.In the interest of full disclosure, I don't have access to the latest API RP-500. But the 2002 edition doesn't consider the area inside the dike Division 1. See Figure 7.
The number of hours per year is neither an NFPA/NEC nor API concept; it is an IEC concept. You will note that it isn?t mentioned in either Section 500.5(B)(1), or Section 505.5(B)(1) or (2) - even in the FPN/INs. Unless it was snuck in in the latest API RP-505 [2011] it isn?t there either. If it is, it still isn't an NFPA/NEC concept.
When it was first proposed for RP-505 I kept it out because it is one of the fundamental differences between US domestic Divisions/Zones and IEC Zones. US Divisions/Zones are defined in terms of possibility; i.e., it could happen under the specified circumstances; i.e. under ?normal? or certain ?abnormal? operating conditions. The problem is normal is undefined. If I really needed to, I can show you Division 1 locations that are never hazardous in their ?normal? operating lifetimes. As an interesting aside, look up 500.8(B)(5) as ?normal? is applied to motors. (Technically, you can't start a motor in a classified location)
IEC Zones are defined in terms of probability ? that?s where the hours per year come in and even then they vary from jurisdiction to jurisdiction. Assuming a year is roughly 8000 hours, the most common is 1000 hrs/yr or more is Zone 0; 100 hrs/yr or more is Zone 1; 10 hrs/yr (or 1 depending on the jurisdiction) is Zone 2. A few (very few) IEC jurisdictions will say any probability is Zone 2, but that is rare.
The key is "normal"To me Division 1 means the flammable concentration can exist under normal operating conditions.
Yes, occasionally things do head for the toilet. You never run - well, unless the fire is licking at one's rear.:blink: Set down the tools. Walk quickly out. Hit the stop switch on the welding machine, which hopefully is on top of the dike, or the other side of the dike.To me Division 1 means the flammable concentration can exist under normal operating conditions. Yes a lot of the time it is clear, but how fast can it change, how fast does the meter react, how fast can you run? ...
In the case where flammable vapors are there all the time - you're right. However, in the example of the tankyard operator gathering readings: She verifies no tank loading, takes a monitor, verifies clear, walks in and gets the readings.... The only document is the definition of Division 1 and it says that a flammable concentration may exist under normal operating conditions. Based on that I don't see how an employeer can send an employee into the Division 1 area. ...
I'm okay with that as long as you aren't the one with the gun and the badge....I understand that I am being unreasonable here, ...
Fortunatly for me, the crews I've been around knew how to do the work safely regardless of the system....I just don't like how the system works...
That is part of my issue. Yes I am aware that the purpose of the area classification is electrical, but once it is classified it is telling me that there is a hazard and that hazard applies to everything....Area Classification is about electrical installations - not maintenance. However, one perhaps should consider the Area Classification as a guide when doing maintenance. Again the key is 'normal".
That was not clear and while you have not changed the classification on paper, it has been changed. I am aware of work being done in an area where only the specific equipment was "made safe" and the was other equipment in the area that was not made safe...they were still working in a real division 1 location.All of my examples include (or should have included dunce: if I didn't) isolate, drain, clean, ventilate, monitor. Ah, (you say) but that is no longer D1. Well, no one is going to temporarly redline the area classification drawing. Consider the prework similar to energy isolation for electrical maintenance.My new translation of your comments leads me to believe we are not at cross purposes. You are correct, no one should be going into a "normal" D1 area to do maintenance. My response is, "You're right. Clean up, isolate and ... Shutting down (lockout) tanking loading to prevent reliefs is usual. The area is still D1 because area classification is about electrical installations - not maintenance. ...
I would not permit that entry into the Division 1 area.Yes, occasionally things do head for the toilet. You never run - well, unless the fire is licking at one's rear.:blink: Set down the tools. Walk quickly out. Hit the stop switch on the welding machine, which hopefully is on top of the dike, or the other side of the dike.
In the case where flammable vapors are there all the time - you're right. However, in the example of the tankyard operator gathering readings: She verifies no tank loading, takes a monitor, verifies clear, walks in and gets the readings.
I would shake things up if I was.m okay with that as long as you aren't the one with the gun and the badge.
The way you have described it, I think they have worked safely, but that is not always the case, not even sure it is the norm.Fortunatly for me, the crews I've been around knew how to do the work safely regardless of the system.
ice
1 Scope
1.1 PURPOSE
1.1.1
The purpose of this recommended practice is to provide guidelines for classifying locations Class I, Division l and Class I, Division 2 at petroleum facilities for the selection and installation of electrical equipment. Basic definitions given in the 1996 edition of NFPA 70, the National Electrical Code (NEC), have been followed in developing this recommended practice. This publication is only a guide and requires the application of sound engineering judgment.
…
1.1.2 Electrical installations in areas where flammable liquids, gases, or vapors are produced, processed, stored or otherwise handled can be suitably designed if the locations of potential sources of release and accumulation are clearly defined. Once a location has been classified, requirements for electrical equipment and associated wiring should be determined from applicable publications.
Applicable publications may include NFPA 70 (NEC) or API RP 14F. Reference Section 2 for publications for other possible applications.
1.2 SCOPE
1.2.1 This document applies to the classification of locations for both temporarily and permanently installed electrical equipment. It is intended to be applied where there may be a risk of ignition due to the presence of flammable gas or vapor, mixed with air, under normal atmospheric conditions. Normal atmospheric conditions are defined as conditions that vary above and below reference levels of 101.3 kPa (14.7 psia) and 20?C (68?F) provided that the variations have a negligible effect on the explosion properties of the flammable materials.
The following items are beyond the scope of this document:
a. Piping systems used for odorized natural gas used as fuel for cooking, heating, air conditioning, laundry and similar appliances;
b. catastrophes such as well blowouts or process vessel ruptures. Such extreme conditions require emergency measures at the time of occurrence;
c. the suitability of locations for the placement of non-electrical equipment; and
d. classification of locations containing combustible dust, ignitible fibers, or flyings.
...All of my examples include (or should have included dunce: if I didn't) isolate, drain, clean, ventilate, monitor. ...
...That was not clear ....
... Get a meter, check %LEL, ventilate till clear, shut down process if needed. No exceptions. ...
... When I was doing this for a living, one would take a %LEL meter, sniff the area, if clear, go to work, meter stays running right next to the tech. ...
... What one could defend is not putting anyone in harm's way by providing continuous monitoring. The trick is not being able to work while the %LEL is up, but monitoring and not working if the %LEL is up - rather ventilate, clear, then work (if the %LEL is up). ...
... . Provided you bothered to read my posts, you already know how one does this safely - with a couple of extras:
Isolate and clean up the piping.
No tank loading while work is on-going - don't want any venting
Post a fire watch - with an extinguisher or two, and a shovel
... So the practice is to empty the tank, isolate, ventilate, clean. ...
... One drains, isolates, cleans, ventilates. And since one might choose to not have all the equipment in the area locked out, post a fire watch and gas monitor.
I have read them and re-read them...the first one that makes it clear to me as how you do things is post 48. Some of the others imply, but do not make it clear to me.Don -
You certainly have a interesting perspective on making a concept clear.
Perhaps you could consider reading posts before replying.
ice
...Area Classification is about electrical installations - not maintenance. ...
... 1. Electrical area classification is “…for classifying locations Class I, Division l and Class I, Division 2 at petroleum facilities for the selection and installation of electrical equipment.” [1.1.1] ....
... Yes I am aware that the purpose of the area classification is electrical, but once it is classified it is telling me that there is a hazard and that hazard applies to everything. ....
... My primary objection is when using electrical area classification for anything other than for the selection and installation of electrical equipment it usually ends up with the “other” affected parties wanting to reclassify locations. I’ve had structural engineers wanting to use it for determining fireproofing, piping/mechanical engineers wanting to use it for the placement of non-electrical equipment; civil engineers wanting to use it for the permissive use of automobile traffic (“OK- If you can just get the process engineers to train the gases and vapors to stop at the curb”); and now Don wants to use it for toxic PPE ....
... I would not permit that entry into the Division 1 area.
I would shake things up if I was. ....
We are not going to agree on these issues, so I see no need for me to comment.Well, since you know area classification applies to electrical, then you also know it does not apply to everything.
These statements are not a reasoned argument. You not liking it makes no difference as to whether the practices are safe. Paraphrasing rb, a separate hazrdous analysis is needed for hazardous atmosphere - area classification is not a catchall.