- Location
- Mission Viejo, CA
- Occupation
- Professional Electrical Engineer
I’ve been trying to figure out how to address this thread without offending some people that I have a high regard for. Still it seems several commenters are “shooting from the hip.” Hazardous locations aren't "rocket science" but they aren't "just common sense" either.
My initial response (post # 6) was the forum can’t do the electrical area classification for the OP and someone familiar with the process should do it and the rules for Class II receptacles and attachment plugs are found in Section 502.145. Maybe I should have said “someone familiar with the process and qualified to do so should do it.” Otherwise it is still correct.
Since then there have been several comments that have been in error or misleading, usually by trying to apply purely Class I concepts to Class II or by defining who is qualified to do the electrical area classification.
My initial response (post # 6) was the forum can’t do the electrical area classification for the OP and someone familiar with the process should do it and the rules for Class II receptacles and attachment plugs are found in Section 502.145. Maybe I should have said “someone familiar with the process and qualified to do so should do it.” Otherwise it is still correct.
Since then there have been several comments that have been in error or misleading, usually by trying to apply purely Class I concepts to Class II or by defining who is qualified to do the electrical area classification.
- During my term on them, both the API Subcommittee on Electrical Equipment’s Task Force for API RP-500 & 505 and the NFPA Technical Committee for Electrical Equipment in Chemical Atmospheres (NFPA 496, 497 & 499) were made up entirely of the electrical discipline.
- Class II, Division 1 is effectively defined as any Group E; and for Groups F & G, it is a moderate to dense dust cloud or a dust layer of 1/8” or greater. Class II, Division 2 for those Groups is no visible cloud, but a visible dust layer less than 1/8”. Dust collecting techniques can affect the envelopes as well. The general envelopes are shown in NFPA 499.
- LEL is undefined in Class II.
- One concept common with Class I and Class II is "close" to a classified location source isn't enough - you have to draw the line somewhere.
- At one time the NEC required Zone classified locations to be done by a PE; the NEC no longer does but FedOHSA still requires it. It can be done by anyone qualified to do so, no matter what the discipline.
- I definitely consult with other disciplines; but, in the end, it is has always been my name and seal on the electrical area classification drawings.