sfav8r
Senior Member
- Location
- San Francisco Bay Area
I'd like peoples opinions on this. We just did an overhead rewire. As the picture shows, there is a balcony outside of a window on this home. The only access to the balcony is if you crawl out the window and the balcony is only 12 inches deep. It's basically to set plants on. We reused the existing conduit which is in the wall. It exits the face of the building at a point that is 8-1/2 feet above the balcony and 6" to the left of the balcony so it is not OVER the balcony at any point. The inspector failed the inspection because he says there has to be 10' of clearance above the balcony. I feel this is a bad call for several reasons.
1) 230.24(B)(1) says that the clearance must be 10' for the portion of wire that is over the balcony. Since there is no part of the wire over the balcony I don't see the problem.
2) What is the real-world risk here? A person is going to climb out the window, climb up on the railing and grab the wires? They can't even use a ladder because the balcony being only 12" deep wouldn't allow you to lean the ladder at a good enough angle to climb on it.
FYI the wire that crosses over the balcony is the CATV wire. The service drop is next to the down spout and enters opposite the balcony. The 1/2 EMT is being held up just as a reference so you can see how the balcony lines up with the service drop.
What do you think? I plan to speak directly to the inspector and ask him to reconsider (one of my guys was there for the inspection) and if he still feels it's a reasonable call I run it by his boss. I'm just curious if most of you agree that the world won't be a better place if we raise this.
Thanks
1) 230.24(B)(1) says that the clearance must be 10' for the portion of wire that is over the balcony. Since there is no part of the wire over the balcony I don't see the problem.
2) What is the real-world risk here? A person is going to climb out the window, climb up on the railing and grab the wires? They can't even use a ladder because the balcony being only 12" deep wouldn't allow you to lean the ladder at a good enough angle to climb on it.
FYI the wire that crosses over the balcony is the CATV wire. The service drop is next to the down spout and enters opposite the balcony. The 1/2 EMT is being held up just as a reference so you can see how the balcony lines up with the service drop.
What do you think? I plan to speak directly to the inspector and ask him to reconsider (one of my guys was there for the inspection) and if he still feels it's a reasonable call I run it by his boss. I'm just curious if most of you agree that the world won't be a better place if we raise this.
Thanks