- Location
- Massachusetts
Are you an electrical inspector? :?
You should seriously consider.:thumbsup:
Only if the head of the department was Bob Ross.
Are you an electrical inspector? :?
You should seriously consider.:thumbsup:
He never quoted NEC section but rather IRC code but still has yet to show me or provide section he is using to fail it.He was wrong about the gfci needing an egc to work but (depending on what the receptacles were going to feed) he could have correctly pinched you on 250.114 (3) A&B- some things are required to have a egc -whether or not gfci'd.
I agree egc needed per 250 .114 but he is only testing the receptacle..no cord and plug connected equipment is in place here. So that would not applyHe was wrong about the gfci needing an egc to work but (depending on what the receptacles were going to feed) he could have correctly pinched you on 250.114 (3) A&B- some things are required to have a egc -whether or not gfci'd.
He never quoted NEC section but rather IRC code but still has yet to show me or provide section he is using to fail it.
I agree egc needed per 250 .114 but he is only testing the receptacle..no cord and plug connected equipment is in place here. So that would not apply
ask the guy, if it did, then WHY are those "no equipment ground " labels provided w/ the device?![]()
I see where the no GFCI trip with your water situation but explain how an egc would change the outcome of GFCI. Might help an ocpd tjoughno EGC ??? hmmm, her 3prong hairdryer falls into the tub as she dries her hair while sitting in the water. how does the gfi trip? amps leave hot, hits the water, into her, back into water, back to N. amps in = amps out = no trip = shocked her
gfi w/o egc is just bad choice imho.
If there are metal parts in the dryer that are connected to the cord EGC as well as parts connected to hot and neutral, then if there is a grounded EGC there will be unbalanced current even without a person in the circuit.I see where the no GFCI trip with your water situation but explain how an egc would change the outcome of GFCI. Might help an ocpd tjough
odd?Remember that GFCIs detect ground to neutral connections downstream
Why odd?
so, most inspectors use the plug-in type to test, whether it be in the gfi receptacle itself or a downstream std outlet that is attached to the gfi. so in essence the inspector does not have a "test" button on downstream protected receptacles yet they are required to test them if they are GFI'd using the tool they have been given by the AHJ. thus if the other recepts have no egc then s/he will find it to be "faulty" because the tool is perhaps not the tool for the test. the tool they are using verifies egc during the test, etc. it really comes down to educating the AHJ to change their testing equipment and NEC code, etc. until then you have to fight the AHJ, etc.
OUTLET CIRCUIT TESTERS (QCYU)
GENERAL
This category covers portable devices with fixed attachment-plug blades, or probes attached to flexible leads, used to indicate various wiring conditions in 15 or 20 A branch circuits by a pattern of lights or other similar means along with markings or instructions to identify the probable wiring conditions which cannot be determined by the tester.
The devices may include provisions for checking the functions of a ground-fault circuit interrupter (GFCI) connected to the branch circuit, or for indicating that a branch circuit is connected to an arc-fault circuit interrupter (AFCI). .......................
These devices are not intended for use as comprehensive diagnostic instruments.
Exactly the way you did, using diplomacy and knowledge. It's not his fault that some municipality put him into a position he wasn't prepared for.
Roger
Agreed, he obviously did not take the position that he was not to be questioned.and at least he said he would consult others --
I understood-just giving example of where he could have reasonably (and with an actual code ref) tagged you under those specific circumstances in a kitchen-I was thinking about a fridge or freezer.
AFAIK, there is no nothing in the IRC that backs up what he is saying- He is simply wrapped up in the myth about gfcis needing an egc to function- ask the guy, if it did, then WHY are those "no equipment ground " labels provided w/ the device?![]()
OUTLET CIRCUIT TESTERS (QCYU)
GENERAL
This category covers portable devices with fixed attachment-plug blades, or probes attached to flexible leads, used to indicate various wiring conditions in 15 or 20 A branch circuits by a pattern of lights or other similar means along with markings or instructions to identify the probable wiring conditions which cannot be determined by the tester.
The devices may include provisions for checking the functions of a ground-fault circuit interrupter (GFCI) connected to the branch circuit, or for indicating that a branch circuit is connected to an arc-fault circuit interrupter (AFCI). .......................
These devices are not intended for use as comprehensive diagnostic instruments.
a gfi should have a egc at the outlet. the modes of fault are more common to the egc. take it away and now you dont have full coverage of the gfi.
well,
1) see the 1st part i underlined, that is bad verbiage because a "tester" is the tool, a "testor" is the person doing the testing. end in "or" is usually a person when used in this context of a sentence. the same thing when we say "the weldor is using a welder to weld".
2) what exactly is the definition of "comprehensive diagnostic" ? would you argue that to test a 2-wire gfi you need a tester that is a comprehensive diagnostic instrument? QCYU's that short to EGC are built that way to make sure a EGC is there, because its safer to have EGC with GFI, and in most cases a EGC is required.
i agree with you all, but its sometimes hard to convince the AHJ.
The other way to show it works is to take your wiggy and go from the hot Slot to a known ground, it will trip the GFI.
Let's take a standard GFCI receptacle and take it apart. Inside you will find an electronics board (an IC to some of you), a sensor, and a contact. Since the innards of an actual GFCI are quite complicated, I'll use my crude drawing to make things (hopefully) a little more clear.
OK, school is out.
Once again......... having a proper ground terminated on the GFCI does nothing to affect the functionalilty of a GFCI-protected circuit.
Nothing.
Except with TR receptacles you probably can't get the wiggy inThe other way to show it works is to take your wiggy and go from the hot Slot to a known ground, it will trip the GFI.