FionaZuppa
- AZ
- Part Time Electrician (semi retired, old) - EE retired.
I think that electricity will take the path of least resistance. If that path is through me and to ground then I'm in trouble (unless I have GFCI protection). If I expect that current will flow from the hot conductor out and then through my body and then back through the return conductor (neutral) that's going to be a bit hard to figure. If I put a finger of the right hand on the hot and a finger of the left hand on the return that's a problem but that's not easy to do.
Most appliances used in bathrooms and kitchens where GFCI protection is required don't even have a ground to the appliance. They have a 2 wire plug so how would a ground at the receptacle make any difference.
A ground is required for a refrigerator but a frig has a grounded frame with a three wire receptacle.
why is it hard to figure. drop a 3-prong hairdryer (that is connected to a GFI protected EGC capable recept that has a "no EGC" sticker on it) into a "insulated" tub full of very clean water, with you in the tub. some amps go from hot to N, some amps take one of infinite routes through the water, cross through you, and back to N via one of infinite routes through the water. to the GFI all amps are accounted for, you are now dead. if the EGC was there. some amps will bypass GFI sensor and trip out in that 4-6mA range.
all hairdryers seems to have 3-prong and optional built-on GFI unit. my blender, toaster, fridge, washer, dishwasher, mixer all have EGC, my one coffee maker is non-EGC. so i think your statement is backwards, i think some appliances are non-EGC while most others are.
so, in order to use these items the recept needs to be 3-prong, but if the GFI protected wiring is two wire only then the recept should be non-EGC type, not EGC capable w/ "no egc" sticker. if you use sticker on 2-prong recept you are asking for trouble as the user will, as mentioned, break off the EGC pin or use the no-EGC adapter. if the recept is EGC capable and has the "no EGC" sticker, user has no idea what the sticker means, thus has no sense of the hazard they could be exposed to because there is no EGC, what they may get is false sense of full hazard protection because what they see is a 3-prong cap cord going into a 3-prong recept.