That type of box is not permitted to be solely supported by raceways
Isn't there supposed to be an additional cover for that? I could be wrong but if there was I wouldn't have too much issue with it. I have seen similar equipment for dishwashers and booster pumps many times with water able to run everywhere above just like in this photo, but seems they all had an additional cover over the breakers or other control devices so overspray, splashes, etc, were not a direct threat.
250.8 violation. It appears to be a standard 3/8" malleable beam clamp. I have been called by an inspector for stacking the ground lugs, but can't find anything in the code book about it. Anyone?
View attachment 8576
The 250.8 violation is due to the beam clamp not being listed for grounding. As far as the stacking of lugs is concerned, the paint has not been removed, so there is a violation of 250.12. I don't stack grounding lugs, so I'm not savy of the listing instructions for these lugs.
Your welcome. I'm not saying an inspector will agree with me, or I will be able to convince the inspector I am right, but I see some logic there.Thank you for your input, kwired.
Your welcome. I'm not saying an inspector will agree with me, or I will be able to convince the inspector I am right, but I see some logic there.
Most memorable inspection was a fuse box in a shower in an apartment building. The tenant said she had to turn off the water heater in order to take a shower without being electrocuted.
Second most memorable was a duplex receptacle beneath (by about 5") a hose bib on a column.
Maybe if the hose bib valve was leaking during the installation or inspection process?Is this a code violation?
Most memorable inspection was a fuse box in a shower in an apartment building. The tenant said she had to turn off the water heater in order to take a shower without being electrocuted.
Second most memorable was a duplex receptacle beneath (by about 5") a hose bib on a column.
Is this a code violation?
Maybe if the hose bib valve was leaking during the installation or inspection process?
I would at least put an in-use cover on the receptacle under the above condition. But not required by code.
Didn't get a picture of it but went to a house yesterday where they removed a wall and after relocating a couple of wires couldn't get the breaker to stay on. What I saw was a mwbc wire that was ran under a wood floor for about 3". Looked to be from the original rough. Just laid it down on the concrete till it got to the basement and then went down. The crazy part is that the homeowners didn't seem to mind it and had splice on to it with butt connectors and were going to run it an additional 3' under the floor to get it back into the nearest wall. :slaphead: