It's not a NEC violation. The receptacle and its outlet box are accessible without removing part of the structure, and the file cabinet, though heavy, can certainly have its drawers taken out to slide it out of the way.Is it a violation to block access to an unused receptacle by placing a file cabinet in front of it ? This is a commercial property ( office building ) .
:?:? So........every office has the file cabs. in the middle of the room?Thanks for the reply Al . I'm having a little disagreement with our safety department over a file room . They made us remove all of the file cabinets because they were against the wall and covering up the receptacles . Said it was against the NEC . The receptacles were not used btw . Wouldn't be the first time Safety got it wrong .
Equipment. A general term, including fittings, devices, appliances,
luminaires, apparatus, machinery, and the like used as a
part of, or in connection with, an electrical installation.
110.26 (A) Working Space. Working space for equipment operating
at 600 volts, nominal, or less to ground and likely to
require examination, adjustment, servicing, or maintenance
while energized shall comply with the dimensions of
110.26(A)(1), (A)(2), and (A)(3) or as required or permitted
elsewhere in this Code.
Ask the inspector if he would fail a receptacle that is placed behind the refrig.
I would say that a receptacle is not "equipment," in the context of the NEC definition, and it is certainly not likely to require maintenance while energized. So 110.26 is not a player.
I agree with Al. 314.29 allows this installation.
If "Safety" is going to invoke 110.26 Working Space for a receptacle outlet behind a file cabinet, then it must be enforced for a receptacle outlet at any desk, a receptacle outlet at a workbench, a receptacle outlet at the break time countertop, a receptacle outlet for a refrigerator, drinking fountain, etc.Not to be a PITA, but if fittings and devices are equipment how is a receptacle not equipment?
I agree 314.29 allows the installation in the wall.
I don't see how 314.29 has anything to do whatsoever with working space.
As for required to be worked on while energized, I think a good argument can be made that virtually anything can be deenergized to work on it. However, as I understand the rules, it is considered energized work to test to see if a circuit is deenergized, so how would you ever be able to work on anything deenergized since the process of deenergizing it requires you to work on it energized first?
I think I have to give you that one. The definition of equipment includes "devices," and I would call a receptacle a device. But I will stand by my assertion that it is not likely to require maintenance while energized.Not to be a PITA, but if fittings and devices are equipment how is a receptacle not equipment?
Just to keep this on track, the original question was not about working space. It was about blocking access. If there were an item (e.g., a branch circuit panel) that required working space, then blocking access to the panel by putting a file cabinet in front of it would be a violation. Receptacles are not among the things that require working clearance. So blocking access with a file cabinet would not violate 110.26. This is also not a violation of 314.29, since the owner or tenant can gain access without having to remove part of the building.
That would have to be a local amendment.I agree it is a bit absurd, but there is no rule in the NEC that says you can ignore any absurd requirements found there.
110.26 does not use the work "panel" when discussing what requires working space. it says equipment.
the definition of equipment appears to include receptacles to me.
I once made the big mistake of putting a bookcase in front of a GFCI receptacle that fed another, accessible, receptacle downstream. (Old house, GFCI for ungrounded circuits.)Then all counter top receptacles mounted in the back splash are in violation.
Not to mention those behind stoves as well as the previously mentioned refrigerator ones.
Would they accept removing the outlets and blanking off considering there not required by code.