Does NEC allow conduits run through building wood frame as in attached picture?
(it appears large, small conduits and cables all run through structural wood frame), if so, which NEC section is not code compliance?

pvc_cond.jpg
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It is not an NEC issue but rather a building code problem. The holes in the left picture aren't an issue as that is just a block of wood an not structural.
 

retirede

Senior Member
Location
Illinois
It is not an NEC issue but rather a building code problem. The holes in the left picture aren't an issue as that is just a block of wood an not structural.

It’s possible none of it is structural. There appear to be trusses above, so that wall is not likely load-bearing. At any rate, building codes would dictate, not NEC as you stated.
 

anbm

Senior Member
Location
TX
Occupation
Designer
How's about this rule?

300.4(A) Cables and Raceways Through Wood Members.
(1) Bored Holes. In both exposed and concealed locations, where a cable- or raceway-
type wiring method is installed through bored holes in joists, rafters, or wood members,
holes shall be bored so that the edge of the hole is not less than 32 mm (1-1∕4 in.) from
the nearest edge of the wood member.
Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by screws or nails by a steel
plate(s) or bushing(s), at least 1.6 mm (1∕16 in.) thick, and of appropriate length and
width installed to cover the area of the wiring.
 

jap

Senior Member
Occupation
Electrician
I first thought the 2 on the left were PVC,,,, I think they're actually Carflex,,, not that it matters.

JAP>
 

jap

Senior Member
Occupation
Electrician
Definitely rigid PVC; you can see couplings on the elbows above the top plate.
On the 1/2" pvc stubups on the right I do, but, not on the 2 larger one's in the middle.

Maybe I'm missing something.

JAP>
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
On the 1/2" pvc stubups on the right I do, but, not on the 2 larger one's in the middle.

Maybe I'm missing something.
My apologies. I didn't realize which post you were addressing. I agree with your assessment.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
A bit messy, but it looks compliant to me. Wall top plates are rarely weakened by holes.
The IRC requires any hole or notch more than 50% of the width of a top plate in a bearing wall be structurally augmented with a metal strap or continuous sheathing on one side. Obviously not an issue in a non-bearing wall.


I'm not finding anything similar in the IBC, but it would seem like a good practice.

Cheers, Wayne
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The IRC requires any hole or notch more than 50% of the width of a top plate in a bearing wall be structurally augmented with a metal strap or continuous sheathing on one side. Obviously not an issue in a non-bearing wall.
Good to know. Thank you.

I'm sure this one is non-load-bearing, and the holes don't approach 50%.
 

jap

Senior Member
Occupation
Electrician
My apologies. I didn't realize which post you were addressing. I agree with your assessment.

I wish we could see the whole picture.

The 2 larger ones may be panel feeders but if so would like to see how they got all that into flush mount panels with them coming down in separate voids and all.

Maybe a flush mount gutter then down to a couple of flush mount panels?

Lot of speculation.


JAP>
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The 2 larger ones may be panel feeders but if so would like to see how they got all that into flush mount panels with them coming down in separate voids and all.
Perhaps each one makes a 90 into the lower side KO of each panel.
 

jap

Senior Member
Occupation
Electrician
Perhaps each one makes a 90 into the lower side KO of each panel.
The larger flexes coming down would have to cris-cross to get into the side of the panels,otherwise you'd have some sort of 90d fitting hidden behind the sheet rock.

But you're right,,,, I don't think the larger ones could cross each other to get into the panels ,,, there wouldn't be enough room in the void for that to happen.


JAP>
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't think that just because there are trusses that the wall isn't load bearing. It depends on how long the truss is as it may be designed with that wall as a load bearer.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I don't think that just because there are trusses that the wall isn't load bearing. It depends on how long the truss is as it may be designed with that wall as a load bearer.