Color Re-Coding
Re: Color Re-Coding
Yes its true and I should of stated the NEC does not generally require a color code for conductors, to be exactly correct.
The conductor colors as required are:
white/gray-grounded conductor
green-equipment grounding
orange-mid point grounded delta
light blue-IS wiring
brown/orange-health care isolated ground
The last two are specific applications and not well known. But the question comes up so often that my reply is boilerplate.
Re: Color Re-Coding
John, what don't you believe I said? Please explain.
Roger
Re: Color Re-Coding
Hello Dave, it's in 517.160(A)(5).
I guess some here doesn't think it counts since it's in a chapter beyond what they deal with. ;)
Roger
Re: Color Re-Coding
Roger,
Thanks!!
Interesting...... if I'm reading this correctly, the orange conductor is the grounded conductor when it is used in this manner?
For 3-phase systems, the third conductor shall be identified as yellow. Where isolated circuit conductors supply 125-volt, single-phase, 15- and 20-ampere receptacles, the orange conductor(s) shall be connected to the terminal(s) on the receptacles that are identified in accordance with 200.10(B) for connection to the grounded circuit conductor.
How then do we "color" all 4 conductors?
Also, how does this not conflict with 200.6?
Re: Color Re-Coding
Dave none of the conductors are grounded.
That article just tells us the orange conductor will terminate on the receptacle where the grounded conductor would normally terminate.
Now I am going out on a limb, I do not believe there would ever be a forth conductor in these systems.
Roger, what's the real deal? :)
No conflict with 200.6 because of 90.3 :)
Bob
Re: Color Re-Coding
Bob, you are correct. The conductors are phase to phase ie 60 v to 60 v. This system is a true example of an isolated transformer. (secondary winding has no reference to earth or any common point)
Roger
Re: Color Re-Coding
Thanks Roger, what I was really wondering about is if there is ever 4 conductors?
As in 3 hots and a ungrounded common.
And would that common be a neutral? :D
Re: Color Re-Coding
Bob,
no, there would never be 4 conductors as there is never a common in these systems.
With that question in mind, all I could say would be, "Thank Goodness" we don't have a common!!! :D
Roger
Re: Color Re-Coding
Roger
As`far as mentoring or teaching someone "beyond what is normal" in the first 4 chapters, yes I do. But I also tell them that these are special occupancies or special instalations and the rules in chapters 5,6,and 7 only apply to the application,system or occupency specified. 517.160 color code only applies to an isolated power system in a health care facility. That was why I made the statement, use the code as it is inteneded.
Re: Color Re-Coding
Roger
Quote by Roger
Orange, brown, and yellow are specifically required in the NEC for a three phase system.
This is what I was referring to. Where is this requirement?
Re: Color Re-Coding
John, 517.160(A)(5).
Roger
Re: Color Re-Coding
OK,..I have a 4-wire system,coming from the secondary of a utility xfrmr..it's 277/480Y and is coming into the 400A CT cabinet...these are replacement wires due to a fire in the original xfrmr.There were 4-750mcm.Aluminum,THW's and I've replaced them with 4-500mcm.Copper,THHN's...The original markings on these wires were Black,Red,and Blue,and of course,White for the neutral...the inspector for the utility co.said they were marked wrong and that I need to change the colors to Brown,Orange,and Yellow,..White or Gray for the neutral...is this correct..? and where can I see it in "the Book"..?? :D :D
Re: Color Re-Coding
Howya doing Bob,
I was advised to bring this question here,from the ECN page...Thats me, BTW, Ledolectric over here on this page..maybe I should use one name??