Re: Color Re-Coding

Yes its true and I should of stated the NEC does not generally require a color code for conductors, to be exactly correct.
The conductor colors as required are:
white/gray-grounded conductor
green-equipment grounding
orange-mid point grounded delta
light blue-IS wiring
brown/orange-health care isolated ground

The last two are specific applications and not well known. But the question comes up so often that my reply is boilerplate.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Color Re-Coding

John, what don't you believe I said? Please explain.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Color Re-Coding

Hello Dave, it's in 517.160(A)(5).

I guess some here doesn't think it counts since it's in a chapter beyond what they deal with. ;)

Roger
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Color Re-Coding

Roger,

Thanks!!

Interesting...... if I'm reading this correctly, the orange conductor is the grounded conductor when it is used in this manner?
For 3-phase systems, the third conductor shall be identified as yellow. Where isolated circuit conductors supply 125-volt, single-phase, 15- and 20-ampere receptacles, the orange conductor(s) shall be connected to the terminal(s) on the receptacles that are identified in accordance with 200.10(B) for connection to the grounded circuit conductor.
How then do we "color" all 4 conductors?
Also, how does this not conflict with 200.6?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Color Re-Coding

Originally posted by websparky:
Interesting...... if I'm reading this correctly, the orange conductor is the grounded conductor when it is used in this manner?
Dave none of the conductors are grounded.

That article just tells us the orange conductor will terminate on the receptacle where the grounded conductor would normally terminate.


How then do we "color" all 4 conductors?
Now I am going out on a limb, I do not believe there would ever be a forth conductor in these systems.

Roger, what's the real deal? :)

No conflict with 200.6 because of 90.3 :)

Bob
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Color Re-Coding

Bob, you are correct. The conductors are phase to phase ie 60 v to 60 v. This system is a true example of an isolated transformer. (secondary winding has no reference to earth or any common point)

Roger
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Color Re-Coding

Thanks Roger, what I was really wondering about is if there is ever 4 conductors?

As in 3 hots and a ungrounded common.

And would that common be a neutral? :D
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Color Re-Coding

Bob,
what I was really wondering about is if there is ever 4 conductors?

As in 3 hots and a ungrounded common.
no, there would never be 4 conductors as there is never a common in these systems.

And would that common be a neutral?
With that question in mind, all I could say would be, "Thank Goodness" we don't have a common!!! :D

Roger
 

caj1962

Senior Member
Re: Color Re-Coding

Roger
As`far as mentoring or teaching someone "beyond what is normal" in the first 4 chapters, yes I do. But I also tell them that these are special occupancies or special instalations and the rules in chapters 5,6,and 7 only apply to the application,system or occupency specified. 517.160 color code only applies to an isolated power system in a health care facility. That was why I made the statement, use the code as it is inteneded.
 

electricman2

Senior Member
Location
North Carolina
Occupation
Retired Electrical Contractor
Re: Color Re-Coding

Roger
Quote by Roger
Orange, brown, and yellow are specifically required in the NEC for a three phase system.
This is what I was referring to. Where is this requirement?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Color Re-Coding

John, 517.160(A)(5).

Roger
 

ledolectric

Member
Re: Color Re-Coding

OK,..I have a 4-wire system,coming from the secondary of a utility xfrmr..it's 277/480Y and is coming into the 400A CT cabinet...these are replacement wires due to a fire in the original xfrmr.There were 4-750mcm.Aluminum,THW's and I've replaced them with 4-500mcm.Copper,THHN's...The original markings on these wires were Black,Red,and Blue,and of course,White for the neutral...the inspector for the utility co.said they were marked wrong and that I need to change the colors to Brown,Orange,and Yellow,..White or Gray for the neutral...is this correct..? and where can I see it in "the Book"..?? :D :D
 

ledolectric

Member
Re: Color Re-Coding

Howya doing Bob,
I was advised to bring this question here,from the ECN page...Thats me, BTW, Ledolectric over here on this page..maybe I should use one name??
 