also interesting..neutral is bonded indicating service...but conduit is not;
Yes, those line side conductors are service conductors, they tie into a underground 208Y/120 underground network. This is common in many sections of Boston.
the pigtail fuse is priceless also..
That was part of a shunt trip set up that was disconnected at the time of my visit.
same guys did your NM job ??![]()
No,
I especially like the bare ground wire in the top right, under the nail or screw used as a fastener for the box.
That is the grounding of the NM that is part of the shunt trip circuit. The NM leaves this service disconnect and goes up to a "Fire Alarm" pull station in the main lobby. If you pulled the station it would dump the service but it would not contact the FD or trip the buildings fire alarm system. At the time of my visit the shunt power had been killed but the useless pull station remains.
It is worth mentioning this was an identical set up in at least 5 buildings I visited that day.