Art 409.102(B) States "The B phase Shall be that phase voltage having the higher voltage to ground on 3-phase, four wire, delta-connected system" and Art 110.15 requires identification of the phase with the higher voltage to ground with orange or other effective means. Ok
On a four wire Delta secondary where the mid point of the B phase is grounded for 120/240v
Why would we identify the B phase orange when the A phase has the higher voltage to ground with respect to the mid point of the B Phase?
[ April 09, 2005, 01:43 PM: Message edited by: sparks1 ]
Now you bring up an interesting point!Originally posted by jwelectric:
What will I do with 110.15? Hey I got it I will mark it Orange and forget all this other stuff.
Art 409.102(B) States "The B phase Shall be that phase voltage having the higher voltage to ground on 3-phase, four wire, delta-connected system" and Art 110.15 requires identification of the phase with the higher voltage to ground with orange or other effective means. Ok
On a four wire Delta secondary where the mid point of the B phase is grounded for 120/240v
Why would we identify the B phase orange when the A phase has the higher voltage to ground with respect to the mid point of the B Phase?