 - Massachusetts
So what about derating. It is a non issue since there are only 4 current carrying conductor.
I was thinking the same thing.
Derating never crossed my mind. Yeah, someone might plug their Christmas display into it, but do you usually run the a/c in December? (OK, you do in Florida.)
It's not that it is because once you do derate you still are over 20 amp.
Uh, it's an AC unit, we are not restricted to the small conductors ampacify![]()
That has nothing to do with it.
With what? A 4-6 CCC derating on a,12 awg conductor could reduce the ampacity below that which is required for an AC unit.
But are you over the MCA of the unit?
But a circuit with 15/20 amp general purpose 120 volt receptacle outlet(s) is limited to the small conductors ampacity rules. (at least I am pretty certain it is - I did not look to verify)Uh, it's an AC unit, we are not restricted to the small conductors ampacify![]()
I have seen them with MCA and MOCP pretty close to each other. Something like 18.2 and 20.I guess I haven't been around enough mini-splits to know for certain, but your typical unit with an AC compressor that has MOCP of 20 amps usually will not have an MCA much higher then maybe 12 amps - but this would be for typical across the line starting for typical induction type motors, if there is a motor design involved with reduced starting current then you could get the MCA closer to the MOCP
Using one leg of the disconnect doesnt always work out.
The GFI receptacle is not a motor load and the same rules dont apply to it as does the AC Unit.
Although you can upsize the breaker for the feed to AC Unit, if you do, and the overcurrent/short circuit protection is above 20 amps, I dont feel you could tap one leg to feed the receptacle above its rating , unless I'm reading it all wrong.
JAP>
Which opens another can of worms that has been debated here before regarding definitions of feeders and branch circuits - and whether that inline fuse is a branch circuit OCPD or a supplemental device.Pretty much but you could tap the line side and add a inline 20 amp fuse for the receptacle.
Uh, #12 wire implies a 20 amp circuit. :huh: