Is there an exception in the NEC for this?This is about the only place a neutral is permitted to be switched by itself.
Originally posted by ronaldrc:
Side ways and upside down.Didn't mean to change the subject.
I rewired a wood mill machine for a company that rebuilds old ones and resales them.
The electrician that wired the one before me got the company sited for having his start stop push buttons on the common side of the coil. The control transformer was a .5 KVA x1 was 120 hot x2 was the grounded conductor and grounded to the equipment body. Don't know why? But he put the controls on the grounded side this was very dangerous.They give the NEC. article and par. but its been a few years.
Ronald