Re: combo disconnect /motor starter
Magnetic starters are wired for any control voltage. The only problem with 120 is switching the grounded conductor (if it is grounded), this does not present a hazard, nothing is energized that is not intended to be.
I would not want to be the inspector that called for rewiring the starter.
Both wires to the coil will often be the same color, usually black. This is when 240 and 480 control voltage is used. There is no issue for which side the overload switches are located.
Magnetic starters are wired for any control voltage. The only problem with 120 is switching the grounded conductor (if it is grounded), this does not present a hazard, nothing is energized that is not intended to be.
I would not want to be the inspector that called for rewiring the starter.
Both wires to the coil will often be the same color, usually black. This is when 240 and 480 control voltage is used. There is no issue for which side the overload switches are located.