James L
- Kansas Cty, Mo, USA
- Electrician
Seevice passed inspection, he had no comments either way regarding the chase nipplesWhat's the inspectors opinion? Just wondering.
Thinking about it some more, my position as "evolved". As long as the myers hubs are considered bonded to the wireway, the concentrics dont matter as there is generally no need to bond both ends of a raceway, unless the raceway is the fault current path. Did the wireway get bonded to the neutral?Seevice passed inspection, he had no comments either way regarding the chase nipples
Are you telling me the handle ties aren't allowed for MWBCs? Doesn't HOM make a different style for that I should be using? I'll have to look for a double-pole circuit breaker with a common internal trip tie mechanism and swap them out. Not sure HOM makes those, or at least, I've never seen them. Thanks for the heads-up. I don't mind constructive criticism.Only thing I see that you did wrong is use two pole/handle tied breakers for the MWBC's![]()
I’ve never been able to use a bond bushing on a Myers hub, not enough threads, he would have to change to a nipple, and the bond bushing on top.In many juridictions, "myers" hubs installed on services require bond bushings.
Well I was saying that I don't like t handle tie rule and don't follow it when I don't have to.Are you telling me the handle ties aren't allowed for MWBCs? Doesn't HOM make a different style for that I should be using? I'll have to look for a double-pole circuit breaker with a common internal trip tie mechanism and swap them out. Not sure HOM makes those, or at least, I've never seen them. Thanks for the heads-up. I don't mind constructive criticism.
Brady BMP61 but I see now they've redone their part numbering system yet again which will snow ball through our ERP system. Great job, Brady.What label maker did you use on those wires in the panel?
Roger that. It never crossed my mind that tie kits weren't acceptable.....but then again, I've had this desk job for 26 yrs and residential wiring isn't something I get paid to do so it rarely crosses my mind anymore.Well I was saying that I don't like t handle tie rule and don't follow it when I don't have to.
What's the dimensions on the required "running boards" you speak of?If I remember correctly, you would need running boards on both sides of the wire within three feet of the attic access. (I think it was three? Might be five? Can’t remember!)
You've lost me. There are two separate 200A service runs from the pad mount transformer. Each go to their own ATS on the backside of the 2" stub out at the top of each panel. Feeders will shoot from each ATS right through the wall into each panel. What do you mean by the same wireway?You shouldn't have your feeder conductors going back into the same wireway as the service conductors
I think it is 1x4”, I don’t have my code book with me right now. Same as running romex exposed on the bottom of floor joists in a basement.What's the dimensions on the required "running boards" you speak of?
Tie kits are acceptable, he was just saying he didn’t like having to do that.Roger that. It never crossed my mind that tie kits weren't acceptable.....but then again, I've had this desk job for 26 yrs and residential wiring isn't something I get paid to do so it rarely crosses my mind anymore.
Roger that. I'll be the only one in the attic for the most part so I wasn't too worried about it.I think it is 1x4”, I don’t have my code book with me right now. Same as running romex exposed on the bottom of floor joists in a basement.
Cool. I looked for single operator HOM breakers this morning and didn't find any. I typically don't do MWBCs and thought it would be something different I could use to save a few conductors. They are all in the kitchen and will have GFI's on each one. I hope being all GFI's the shared neutral doesn't cause them issues. That never crossed my mind until now.Tie kits are acceptable, he was just saying he didn’t like having to do that.
As long as the load side of the gfi isn’t, you’re fine.Roger that. I'll be the only one in the attic for the most part so I wasn't too worried about it.
Thanks for all the feedback.