PbMXer_218
- Largo, Florida
- Licensed Electrician EC
Hello!
I am finishing a commercial project in Florida, a large grocery store. There is a 3 phase, 20 amp 208 v GFCI protected (breaker) circuit feeding a mixer. The mixer is a cord and plug connection. The electrical coordinator is claiming the mixer has some sort of problem with Square D QOB breakers and they have problems with it tripping the breakers at other store locations with Square D gear but not with other brands of gear for example Siemens. I have not witnessed this personally. We explained, removing the code compliant breaker and installing a non GFCI breaker was not something we were willing to do for safety reasons and the code compliance issue. Now he is asking for us to still remove the GFCI breaker and install a non GFCI breaker, install a 3 pole disconnect adjacent to the mixer, and hard wire the mixer to the disconnect. My question here is, does this method (hard wired to a disconnect) alleviate the GFCI requirement? I have read 210.8(b) (2023) and it does not clearly state this. At least I am not comprehending it in this way. In my opinion, I still believe it is still required to be GFCI protected. Any help is greatly appreciated. Thanks