I am starting this thread to avoid taking away from another threads on branch circuits.
110.8 Wiring Methods.
Only wiring methods recognized as suitable are included in this Code. The recognized methods of wiring shall be permitted to be installed in any type of building or occupancy, except as otherwise provided in this Code.
210.3 Rating.
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire branch circuit shall be permitted to be considered as multiple circuits. All conductors shall originate from the same panelboard.
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
ARTICLE 225 Outside Branch Circuits and Feeders
225.1 Scope.
This article covers requirements for outside branch circuits and feeders run on or between buildings, structures, or poles on the premises; and electric equipment and wiring for the supply of utilization equipment that is located on or attached to the outside of buildings, structures, or poles.
FPN:For additional information on wiring over 600 volts, see ANSI C2-1997, National Electrical Safety Code.
225.2 Other Articles.
Application of other articles, including additional requirements to specific cases of equipment and conductors, is shown in Table 225.2.
225.7 Lighting Equipment Installed Outdoors.
(A) General. For the supply of lighting equipment installed outdoors, the branch circuits shall comply with Article 210 and 225.7(B) through (D).
(B) Common Neutral. The ampacity of the neutral conductor shall not be less than the maximum net computed load current between the neutral and all ungrounded conductors connected to any one phase of the circuit.
What I believe is common neutral circuits and multi-wire circuits are different animals. You are given permission to use multi-wire circuits if they are designed as defined above.
A circuit utilizing a neutral that is common to one or more others circuits not meeting the definition of a Multi-wire circuit is limited by the code to specific applications
David
110.8 Wiring Methods.
Only wiring methods recognized as suitable are included in this Code. The recognized methods of wiring shall be permitted to be installed in any type of building or occupancy, except as otherwise provided in this Code.
210.3 Rating.
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire branch circuit shall be permitted to be considered as multiple circuits. All conductors shall originate from the same panelboard.
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
ARTICLE 225 Outside Branch Circuits and Feeders
225.1 Scope.
This article covers requirements for outside branch circuits and feeders run on or between buildings, structures, or poles on the premises; and electric equipment and wiring for the supply of utilization equipment that is located on or attached to the outside of buildings, structures, or poles.
FPN:For additional information on wiring over 600 volts, see ANSI C2-1997, National Electrical Safety Code.
225.2 Other Articles.
Application of other articles, including additional requirements to specific cases of equipment and conductors, is shown in Table 225.2.
225.7 Lighting Equipment Installed Outdoors.
(A) General. For the supply of lighting equipment installed outdoors, the branch circuits shall comply with Article 210 and 225.7(B) through (D).
(B) Common Neutral. The ampacity of the neutral conductor shall not be less than the maximum net computed load current between the neutral and all ungrounded conductors connected to any one phase of the circuit.
What I believe is common neutral circuits and multi-wire circuits are different animals. You are given permission to use multi-wire circuits if they are designed as defined above.
A circuit utilizing a neutral that is common to one or more others circuits not meeting the definition of a Multi-wire circuit is limited by the code to specific applications
David