Those images were posted while I was writing what I did before. Important thing I left out (and mostly because this is something I never have to deal with) that was pointed out is displacement. That I'm assuming is the difference in angle between the primary and secondary as drawn in that image. Get the displacement and draw same thing I described with the displacement factored in and you get same thing that was drawn there. Again the grounded conductor is common to both systems if anything because they are bonded together, though I'm sure there is a little more then that to it.interesting point... I am curious myself. I know that the words Phase and Time are actually the same thing as they relate to voltage but I was under the impression that the two systems were in synch. Any opinions?
I will give you a description that will hopefully help you draw your own.
Both the 277 and 120 volt systems will have a common point at the grounded conductor.
Establish that point then draw a line 277 units long. Then draw another line 120 units long from that same point at a 120 angle (the phase angle) If on same phase you will draw the 120 volt line in the same direction as the 277 volt line. The distance between the ends of these two lines (in same units of measurement) will be same as the voltage would be. The same phase application would be simplest to figure out 277-120= 157 volts.
I can see this may be more complicated by wye-wye transformer compared to delta-wye transformer or even a single phase transformer connected to two phase conductors on the primary as compared to connecting it phase to neutral, as the vectors are probably a little more complex to figure out, but hopefully this gives enough understanding to know why the voltages turn out the way they do. Most field electricians would never need to know much more then this on a regular basis.
Those images were posted while I was writing what I did before. Important thing I left out (and mostly because this is something I never have to deal with) that was pointed out is displacement. That I'm assuming is the difference in angle between the primary and secondary as drawn in that image. Get the displacement and draw same thing I described with the displacement factored in and you get same thing that was drawn there. Again the grounded conductor is common to both systems if anything because they are bonded together, though I'm sure there is a little more then that to it.
Things do not work that way, especially since most of the step down transformers we use are configured as Delta-Wye. The secondary side Phase A winding sits opposite a primary winding that is connected to the 480 volt Phases A and B. So there really is no correlation between what is called Phase A on the primary and secondary sides. In addition, the Delta-Wye creates a 30 degree shift in phase, so that the primary and secondary sides are not in phase with each other.Phase A from the 480 system and phase A from the 208 system.
Things do not work that way, especially since most of the step down transformers we use are configured as Delta-Wye. The secondary side Phase A winding sits opposite a primary winding that is connected to the 480 volt Phases A and B. So there really is no correlation between what is called Phase A on the primary and secondary sides. In addition, the Delta-Wye creates a 30 degree shift in phase, so that the primary and secondary sides are not in phase with each other.
Don't worry Bob, think "engineer" and how a single winding transformer can create a thread of 32,000 posts.I am left extremely confused. :?
As long as you started with the same primary source, and you get the correlation of which phase is which correct, then yes. Keep in mind that changes in loading conditions can also cause phase shifts, so my comments are based on unloaded conditions.Would 2 delta-Wyes create the same phase shift when comparing secondary to secondary?
As long as you started with the same primary source, and you get the correlation of which phase is which correct, then yes. Keep in mind that changes in loading conditions can also cause phase shifts, so my comments are based on unloaded conditions.
Winnie and I are not in disagreement. If a 277V signal and a 120V signal are indeed in phase with each other, or are nearly so, then the voltage between them would be below 300, as you correctly surmised, and as Winnie confirmed. My point is that you can't really look at what is named "Phase A" on the 480/277V side and what is named "Phase A" on the 120/208V side and say that they are cousins (i.e., that they will be close to being in phase with each other).It seemed Winnie agrees with me and Charlie does not. I am left extremely confused.
Isn't that the earlier mentioned "displacement". Once you figure out what the displacement is, draw your two systems on top of one another with the applicable angle differential between them. If done to scale the distance between any two points is going to be representative of the actual voltage between those pointsIn addition, the Delta-Wye creates a 30 degree shift in phase, so that the primary and secondary sides are not in phase with each other.
Winnie and I are not in disagreement. If a 277V signal and a 120V signal are indeed in phase with each other, or are nearly so, then the voltage between them would be below 300, as you correctly surmised, and as Winnie confirmed. My point is that you can't really look at what is named "Phase A" on the 480/277V side and what is named "Phase A" on the 120/208V side and say that they are cousins (i.e., that they will be close to being in phase with each other).
Winnie and I are not in disagreement. If a 277V signal and a 120V signal are indeed in phase with each other, or are nearly so, then the voltage between them would be below 300, as you correctly surmised, and as Winnie confirmed. My point is that you can't really look at what is named "Phase A" on the 480/277V side and what is named "Phase A" on the 120/208V side and say that they are cousins (i.e., that they will be close to being in phase with each other).
Don't worry Bob, think "engineer" and how a single winding transformer can create a thread of 32,000 posts.
Roger
I can look at any way I would like to.
You must have assumed I was saying in phase when I was saying the phase.
There are both 480 and 208 conductors labeled phases A, B & C. the voltage between the same letter phases will be less than 300.
How would you have worded it in laymen terms?
There are both 480 and 208 conductors labeled phases A, B & C. the voltage between the same letter phases will be less than 300.
How would you have worded it in laymen terms?
So not knowing the phase angle relationship between the 120V and 277V in the switch box, it would be correct to require a barrier between the switches because the "possibility" to exceed 300V between the switches exists.
Sent from my iPhone using Tapatalk
I am going to have side with Charlie on this one...
The point that charlie is making is that the phase labeled "480V A" and the phase labeled "208V A" have no specified phase relation. They might be 0 degrees apart, they might be 150 degrees apart.
so installing a divider would be a good practice.