Now that you have thrown in the towel, I will make one more attempt at clarity.Well I know when to throw in the towel, I would be lying if I said I fully understood what you all are telling me but I have to accept it regardless.
If the 480Y/277 and the 208Y/120 services are produced by POCO transformers of the same vector group, fed by the same primaries, and somebody went to the trouble to match phase labels when all they were required to do was match rotation, then A will be parallel to A, etc. But can you rely on that? Probably not.
If one of the two voltages was derived by a transformer from the other, the odds that they are in phase drops even farther.
Both systems will still have A,B,C labels because it is hard to find A+30degrees, B+30degrees, C+30degrees labels these days.