Re: Common trip required for d/w & disposal?
jwel: If you take a look at the NEC Handbook, 240.20, the handbook goes into a rather thorough discussion on the difference between a 'common trip' and a 'common disconnect'. The first requires a factory assembly, the 2nd permits a field assembly (field installed handle ties).Originally posted by jwelectric:
A handle tie mignt not fulfill this requirement.210.4 Multiwire Branch Circuits.
(B) Devices or Equipment. Where a multiwire branch circuit supplies more than one device or equipment on the same yoke, a means shall be provided to disconnect simultaneously all ungrounded conductors supplying those devices or equipment at the point where the branch circuit originates.