ron
- New York, 40.7514,-73.9925
ASCO 940 Automatic Transfer Switch with in-phase monitoring.
Hospital tests ATS with generators running to reduce outage time to loads. If the in-phase monitoring is functioning properly, the transfer happens only when the sources are within 10 degrees of sync.
With the belief that the sources are sync'd, the ATS has an open transition condition (break before make) for about 20-30 electrical cycles.
Would you expect significant inrush on a typical air compressor to blow fuses sized at 2 x FLA?
It is a new install and it happens randomly on occasion from utility to gen and from gen to utility.