Doesn't the NEC and an inspectors jurisdiction stop at the premises wiring?
If this is not correct please give me a code reference where an inspector can tell you what you can or can not plug in.
If this was hard wired I would agree. But it is not.
Mike, consider the following:
			400.7(B) Attachment Plugs. Where used as permitted in 400.7(A)(3), (A)(6), and (A)(8), each flexible cord shall be equipped with an attachment plug and shall be energized from a receptacle outlet.
If the code stopped at the receptacle, then this sentence would be a paradox.
410.62 would be referencing a luminaire that is outside the scope of the NEC. 422.16 would be referencing a void.
Is there no range or dryer in a dwelling unit if they are cord and plug connected? How do we calculate their loads by 220? Do we just leave them out?
			Point is just that. We have no idea what will get pluged in.
Well, if you've got a series of desks with little bays all dedicated for computer towers, with the towers on site and pictures of little computers all over the prints and elevations, then I suppose one could take a leap and assume computers are getting plugged in, ey?
			If this inspector is stupid enough to not know the name plate is just a peak then he needs find another job.
If the NEC is too stupid to have an allowance built in for this, or a method for determining how to size these circuits expressly spelled out, then I suppose we can blame the NEC for being incomplete and try to remedy that.
As it stands, 220.14(A) is pretty clear:
			(A) Specific Appliances or Loads. An outlet for a specific appliance or other load not covered in 220.14(B) through (L) shall be calculated based on the ampere rating of the appliance or load served.
I don't have all the answers, but I am not seeing a real concrete code answer to get the OP out of the problem. As I see it, it's not the electrician's problem anyway, it is the engineer's. Let them duke it out.