Ron co-wrote an article about this subject, maybe he can post a link to it?
I was always under the impression that this was the heart of the advantage of 645.ron said:Dave,
The types of raceway permitted are also slightly different when you compare 645.5(D)(2) and 300.22(C)
ramsy said:The equipment AC units were bolted to and fed from the floor. There may have been small air deflectors or scoops, but no ducts under the raised floor and lots of chilled forced air from those AC units blasting us around under there. I remember being the only JW that could stand hammer drilling, & strapping raceway in front those 40F wind tunnels. I doubt there was any need for a separate environmental air system overhead, and I didn't see any ducts connecting ceiling to floor.
Sure you can, go back to page one and read my response. Installers/technicians do it all the time That is the beauty of 645, ignorance of the concept generates millions of dollars of unnecessary retrofits making us engineers wealthy and employed.ron said:In a high density datacenter, you can't put everything below the raised floor, because it will block the distribution of cold air.
Tori said:The gas fire suppresion you speak of , what type is it ?