NFPA 75 is not a code in most jurisdictions, just a standard (not requiring compliance)
jjs said:high density data centers are not able to be cooled by underfloor cooling alone. In rack cooling is required. Blade servers generate way too much heat per SF to cool properly with in floor only. You get hotspots in the rack itself. Data center design actually goes in cycles, so something in that 1990 document will eventually come back in to mainstream.
Also liquid cooled computers such as the old mainframes were are becoming more popular as power densities go up.
zbang said:I rather like the idea of an EPO, but at a minimum it should be a flush button, not a mushroom, and it had better have a plastic cover over it. Even better is two buttons next to each other wired in parallel, then a single button failure or accidental press won't bring everything down. Don't know how most AHJs feel about this, though.
Regards cooling, we're now seeing 10+kw per rack, and it's still going up.
bwyllie said:the 20kw per rack, is that measured or nameplate? i would be interested what the actual measured load is of a blade server compared to its nameplate data.
tmillard said:I am still going to have an EPO in my room but it won't shut off the telemetry rack.
Tom
tmillard said:I am still going to have an EPO in my room but it won't shut off the telemetry rack.
Tom
jjs said:Also liquid cooled computers such as the old mainframes were are becoming more popular as power densities go up.
bhsrnd said:Also, I agree with what tallgirl said. In most environments with blade chassis the likelyhood of that chassis to be 100% pegged out for utilization is slim. Most data centers with blade chassis may see a 50% utilization per chassis (even when fully populated) which means you won't come close to the potential nameplate kW.
bwyllie said:the 20kw per rack, is that measured or nameplate? i would be interested what the actual measured load is of a blade server compared to its nameplate data.
tallgirl said:I could easily put 15kW in a blade server rack if I wanted to.
tallgirl said:Just a minor note on the subject of server utilization, there is a trend in the biz towards server virtualization which will drive utilization rates and server sizes higher. So, whereas a blade server might be installed with only half its blades today, in the future it will not only be installed with its full compliment of blades, each with its full compliment of goodies, but it's also likely that each blade will be virtualized into several more servers to make up for any lack of utilization.
bhsrnd said:You are correct and that was one aspect I didn't think of. We have several vitual server installations running, however, our network team has chosen a 3U "beefed up" servers to handle the VM instances versus using our blade centers.
I promise not to ask about the pic.