petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- Semi-retired engineer
Some utilities give you a number that they agree never to exceed. That is the number you should use. It is not based on the equipment supplied at present. Over time the network might get stiffer, they might change out your transformer. But if you use their number it won't be more than their number, even if at present the number they give out far exceeds what the real value of available SCC is. In fact, my understanding is this is built into many of the tariffs these days.Again, as I have said and some others have said as well, there is no such thing as typical.
Utilities run coordination studies. They know the calculated fault current for existing conditions. They also know the worst case scenarios for an area. You just have to reach the right people.
The calculated values will vary by area and the worst case values will vary by area. Across the board typical does not exist.