infinity said:How do you get around the fact that using a CEE is required if there is 20' of 1/2" or larger rebar present in the footing?
No access to it?
wireman71 said:What's the code reference on that?
infinity said:Start with 250.50 first sentence.
augie47 said:My question is, how do you handle the situation if the footer has been poured, perhaps the foundtaion & framing set before the electrician shows up and discovers the CEE was not made accessible or had no attachment ?
augie47 said:The requirement for the CEE is just about to hit TN (we have been on 2002). My question is, how do you handle the situation if the footer has been poured, perhaps the foundtaion & framing set before the electrician shows up and discovers the CEE was not made accessible or had no attachment ?
We have more "dingbats" doing concrete work in this county as we do "homeowner" electrcians. Without a doubt, I am going to find this situation. Seems disturbing an existing footer would brig about an unwanted liability.
iwire said:Here in MA the State building dept sent out a flier to all registered GCs explaining that if they will have rebar in the footing they must hire an EC to pull a permit run a GEC to the rebar and then have it inspected by the electrical inspector.
wirebender said:Couldn't they just stub a 1/2" rebar out the side of the foundation?
georgestolz said:As I read the OP, under the 2008, then by 250.53(A)(3) we would only have to use one or the other CEE, not all of them, IIRC. Are we all agreed on that?
The 2008 is in the car, but that's how I remember the section being reworded.
infinity said:Around here the building inspector must inspect the footing before it's poured. He's also responsible for inspecting the CEE requirement.
infinity said:He's also responsible for inspecting the CEE requirement.
iwire said:This makes no sense to me at all.
Why not let the pool installers bond the pool they install and have the building inspector look at that as well?
I see no good coming from giving away NEC work to other trades and inspectors.
Wouldn't a tie between the rebar and the anchor bolts be simpler and better than running a copper conductor into the concrete. Running stranded copper wire into the concrete without a waterstop would also provide a place for corrosion to start.iwire said:No, here the electrical inspector must look at the re-bar to verify NEC compliance if the rebar is to be used for an NEC application.
Besides, I am not sure the local building department would allow rebar to poke out of the footing. That is a place for corrosion to start breaking down the footing.