Hi Guys -
I have a customer who is asking if it is OK to run our equipment at 166 AMPS.
This is oil field equipment specifically I am asking about the Surface Cable - it is a Southwire #2 MC-HL MV-105 Shd. Cable with a rating of 154 amps in air and 190 direct burial. Copied directly from the Southwire Data sheet "+Ampacities are based on the NEC, 2008 Edition. Direct burial ampacities are based on table 310.83 three-conductors within an overall covering directly buried, 105°Cconductor, 20°C earth ambient temperature. In air ampacities are based on table 310.71 three-conductors within an overall covering in free air, 105°C conductor, 40°C
ambient temperature."
I am interested in the in air rating - I understand that the rating was based on a 40C ambient temperature - now my question is - how do I determine what this rating is if my ambient temperature never exceeds 30C?
Is there a simple formula that I can plug the conductor temp (105 C) along with the "new ambient temp" to determine what the ampacity rating should be?
Here's the link to the actual cable I am working with for reference.
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet137
Thank you guys in advance!
I have a customer who is asking if it is OK to run our equipment at 166 AMPS.
This is oil field equipment specifically I am asking about the Surface Cable - it is a Southwire #2 MC-HL MV-105 Shd. Cable with a rating of 154 amps in air and 190 direct burial. Copied directly from the Southwire Data sheet "+Ampacities are based on the NEC, 2008 Edition. Direct burial ampacities are based on table 310.83 three-conductors within an overall covering directly buried, 105°Cconductor, 20°C earth ambient temperature. In air ampacities are based on table 310.71 three-conductors within an overall covering in free air, 105°C conductor, 40°C
ambient temperature."
I am interested in the in air rating - I understand that the rating was based on a 40C ambient temperature - now my question is - how do I determine what this rating is if my ambient temperature never exceeds 30C?
Is there a simple formula that I can plug the conductor temp (105 C) along with the "new ambient temp" to determine what the ampacity rating should be?
Here's the link to the actual cable I am working with for reference.
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet137
Thank you guys in advance!