110.40 termination limitations
based on tables 310.60(C) (67 thru (86)
ref 310.60(C)(67) for allowable ampacities (hence termination amps)
a note says refer to 310.60(C)(4) for temp adjustments
Using (67) for example only
so for example a 2001-5000 vac #2 cable is good for 160
if ambient is <10 then 1.26 x 160 = 202
and the 90 degree terminations are acceptable
same applies to the cable
bear in mind that although ampacity is increased operating temp is not
still 90
based on tables 310.60(C) (67 thru (86)
ref 310.60(C)(67) for allowable ampacities (hence termination amps)
a note says refer to 310.60(C)(4) for temp adjustments
Using (67) for example only
so for example a 2001-5000 vac #2 cable is good for 160
if ambient is <10 then 1.26 x 160 = 202
and the 90 degree terminations are acceptable
same applies to the cable
bear in mind that although ampacity is increased operating temp is not
still 90