210.5 Identification for Branch Circuits.
.
(C) Identification of Ungrounded Conductors. Ungrounded
conductors shall be identified in accordance with
210.5(C)(1) or (2), as applicable.
(1) Branch Circuits· Supplied from More Than One
Nominal Voltage System. Where the premises wiring system
has branch circuits supplied from more than one nominal
voltage system, each ungrounded conductor of a branch
circuit shall be identified by phase or line and system at all
termination, connection, and splice points in compliance
with 210.5(C)(1)(a) and (b).
(a) Means of Identification. The means of identification
shall be permitted to be by separate color coding, marking
tape, tagging, or other approved means.
(b) Posting of Identification Means. The method utilized
for conductors originating within each branch-circuit
panelboard or similar branch-circuit distribution equipment
shall be documented in a manner that is readily available or
shall be permanently posted at each branch-circuit pane]board
or similar branch-circuit distribution equipment.