What's wrong with using black and white for 277?How many shops here use black/white/green MC cable for 277V lighting circuits![]()
Roger
What's wrong with using black and white for 277?How many shops here use black/white/green MC cable for 277V lighting circuits![]()
What's wrong with using black and white for 277?
Roger
Because........when you have two system voltages present, we are supposed to mark the panels with the system voltages and the corresponding colors used. 99.9999% of the time, black/white/green will correspond with 120/208 system voltages. So those 277V systems using black/white.green will be wrong.
Absolutely nothing is wrong with it as long as the conductors are somehow marked at every panel, device, and splice with something that distinguishes them from 120/240 or 208Y/120.What's wrong with using black and white for 277?
Roger
So being that you are talking about a cable assembly you simply re-identify the black and white to whatever colors you need.
Roger
Agreed but doesn't change anything as far as the code requirements and a qualified person wouldn't need it.Yeah, but I bet nobody takes the time to do that at every switch box/j-box/light fixture whip.
Absolutely nothing is wrong with it as long as the conductors are somehow marked at every panel, device, and splice with something that distinguishes them from 120/240 or 208Y/120.
And that means of identification is suitably made public.
Oh yeah, and as long as the white is only used for a grounded conductor, so no 480 loads fed by it. Or reidentify the white since it is a cable.
Agreed but doesn't change anything as far as the code requirements and a qualified person wouldn't need it.
Roger
I'm a "qualified person" and I recently did a remodel that was done entirely in MC cable originally from day one. Trying to trace out existing circuits was a PITA, since all the cable used was of the 120/208 color variety and all buried in the walls or attic. No boxes were marked 120V or 277V, it was a complete crapshoot as to what voltage was inside the box, all using black/(red)/white/green.
So IOW's it's a safe bet that you wish they would have complied with all identification rules. :thumbsup:
Roger
How many shops here use black/white/green MC cable for 277V lighting circuits![]()
Absolutely nothing is wrong with it as long as the conductors are somehow marked at every panel, device, and splice with something that distinguishes them from 120/240 or 208Y/120.
And that means of identification is suitably made public.![]()
Don't know if this applies to branches
424.35
1 120 V Yellow
2 208 V blue
3 240 V red
4 277 V brown
5 408 V orange
You can do that as long as you show the method of re-identification on the sheet at each panel that shows what methods are being used to identify the conductors as to phase and voltage.So being that you are talking about a cable assembly you simply re-identify the black and white to whatever colors you need.
Roger
Which is what I stated in post #3You can do that as long as you show the method of re-identification on the sheet at each panel that shows what methods are being used to identify the conductors as to phase and voltage.