Conductor in parallel

Status
Not open for further replies.

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
Okay... I'll assume. What does 250.32(A) Exception have to do with the EGC?
Perhaps i'm wrong, I would think the fire pump and chiller would be a branch circuits & meet the exception of 250.32(a).
 

Smart $

Esteemed Member
Location
Ohio
Perhaps i'm wrong, I would think the fire pump and chiller would be a branch circuits & meet the exception of 250.32(a).
Even as branch circuits, the difference made by 250.32(A) Exception is that no grounding electrode system would be required at the building or structure served. An equipment grounding conductor run with the branch circuit conductors would still be required.
 

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
Even as branch circuits, the difference made by 250.32(A) Exception is that no grounding electrode system would be required at the building or structure served. An equipment grounding conductor run with the branch circuit conductors would still be required.
Sorry sir, but that was my post #37....:D
 
Status
Not open for further replies.
Top