I had an inspection today, rough-in for a bathroom remodel. It's a long way from the panel to the bathroom (about 80 feet). One of the circuits is for a heated floor. It draws 5.4 Amps. I put it on a 15 Amp breaker, on its own circuit. Because of the distance from the panel to the bathroom, I ran 12 AWG most of the way, through the basement and crawl space in EMT, then transitioned to 12/2 NM-B to fish up through the walls to the bathroom. I hit a junction box in the bathroom for the main bank of switches, then there's a very short run of 14/2 to the box for the heated floor thermostat.
The inspector said I can't have a 12 AWG wire in the panel on a 15 Amp circuit if any part of my run is 14 AWG. He said the next guy could come in and think the whole circuit is 12 AWG and change the breaker to a 20 Amp.
In this case I increased the wire size to avoid voltage drop. In other cases I've increased wire size because of high ambient temprature of conductors run through an attic.
Is the inspector right? Must the wire guage in the panel correspond exactly the breaker size? This doesn't make any sense to me. Why can't the wire ampacity exceed the breaker size? Would appreciate your help.
Thanks,
David