Oh yeah. That's because the lugs or breaker terminals will not be rated for 90C right?
I was jumping the gun because USE-2 is rated for 100 amps at #2
You got it now. Good Luck
Here is some info for USE 2 Here is the
pdf.
Detail Description
or Construction
Conductor
Compact Stranded Aluminum
Alloy 8000 Series per ASTM B-801
Insulation
UL 44 and UL 854 recognized
Cross-linked Polyethylene
Application
The product can be installed as
general purpose building wire, used in service entrance, feeders and branch circuits applications for residential, commercial, industrial and transportation environments for permanent installations utilizing 600 volts or less. Suitable for directly buried installations and can be used in environments where superior insulation toughness and chemical resistance is required.
The product high resistance to humidity makes this cable suitable for wet locations,
for outdoors and for weather resistant use.