I agree that there's not enough information...namely the OCPD rating. I'm guessing the want you to assume a 50A OCPD for a 48A load. That would make the correct answer #3awg.
Edit: On second thought, if they're asking for the minimum conductor size, that would imply the minimum possible ocpd size...so still #3
Edit: On second thought, if they're asking for the minimum conductor size, that would imply the minimum possible ocpd size...so still #3