I think my reaction about antennas comes from your use of "generated" instead of induced. I was thinking there's something else being added to the system. I could call a generator an inducer but it's unorthodox.
I've reread your post and I should have understood what you were saying the first time.
It only takes 2.65 millihenrys to raise the impedance 1 ohm at 60 cycles.
After doing the math I think it makes sense to shunt the conduit.
Al'
I think my reaction about antennas comes from your use of "generated" instead of induced. I was thinking there's something else being added to the system. I could call a generator an inducer but it's unorthodox.
I've reread your post and I should have understood what you were saying the first time.
It only takes 2.65 millihenrys to raise the impedance 1 ohm at 60 cycles.
After doing the math I think it makes sense to shunt the conduit.