Conduit fill - Three #8awg plus one #10awg in 1/2 EMT?

Status
Not open for further replies.
Location
California
Occupation
Builder
I'd like to use an existing underground 1/2" EMT conduit to run a 50 amp sub panel. The 1/2" is rated for three #8awg wires. I'd like to also pull a #10awg ground wire along with the three #8's. This calculates to a 40.6% fill, barely exceeding the nominal 40%. Will it pull? Is it safe? Thanks :)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Safety is not something we can determine.... It would not be compliant --If that emt is underground I wonder how rusty it is inside. It may be a hard pull.
 

Beaches EE

Senior Member
Location
NE Florida
Occupation
Electrical Engineer / Facilities Manager
You'll need 3/4 (PVC) for that and often 1" is used in these applications in case of future expansion.
 
Location
California
Occupation
Builder
I sure wish this existing underground conduit was pvc and at least 3/4, but alas 1/2 EMT is what I have to work with. My pull rope went through easily, tied to the old wires (three #12awg) when I pulled them out. So the conduit itself is viable. Just not sure how the extra 1/2% of fill will impact the new pull. 358.10 allows EMT for underground.
 

Beaches EE

Senior Member
Location
NE Florida
Occupation
Electrical Engineer / Facilities Manager
Non-compliant is just that. I would not design or recommend an installation that does not meet code.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
... emt is underground I wonder how rusty it is inside. ...
That's going to depend on local conditions. Out in the desert, it might be fine. Close to the ocean, it might soon be nothing but a vestigial line of orange-ish soil.

But will it pull? That depends on a lot of factors, including the number of unseen underground turns. Do everything you can to make it easier -- remove all the kinks & braids, band the wires together periodically, use a funnel and have a helper maintain a constant tension & smooth feed during the pull.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
To make the smallest pulling head, measure the conductors at twice the required length, fold them in the middle, strip the insulation and attach the stripped part to the pulling rope.
 
Location
California
Occupation
Builder
Well it's going to take all the tricks I can learn and an artisanally crafted pulling head but I think it will work. I sent my endoscopic camera down the pipe today and the cuts/transitions are not as deburred as one would like, but the conduit looks pretty good, not terribly rusty as far as the camera went, even though the knot in my pull rope squeegeed water out of the conduit. I plan to: use pull string instead of the poly rope I had on hand, pre-lubricate the conduit, use a funnel to get tons of lube in there while pulling, and get a helper to pull so feed end is well tended even though this is only a 30' run.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
With a 30' pull and water, I predict you won't need any lube. Just keep the wires in the same position.
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
358.10 allows EMT for underground.
I'm pretty sure that code mentioned is for any Emt to be encased in concrete when underground or that it is wrapped in a corrosive proof rubber tape.
358.10 when in accordance with 358.10 (B) (1) (2) / (C) (D). Emt rusts and falls apart after several years if simply buried in dirt.

Why not run a # 12 Ground, I'm pretty sure you can size down 2 times on a branch system. Its just a relief valve for fault. Just a thought.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I'm pretty sure that code mentioned is for any Emt to be encased in concrete when underground or that it is wrapped in a corrosive proof rubber tape.
358.10 when in accordance with 358.10 (B) (1) (2) / (C) (D). Emt rusts and falls apart after several years if simply buried in dirt.

Why not run a # 12 Ground, I'm pretty sure you can size down 2 times on a branch system. Its just a relief valve for fault. Just a thought.
Take a look at table 250.122
 

Jon456

Senior Member
Location
Colorado
If it's only 30 feet, why not dig it out and replace it with 1" PVC? Yes it's more work and will cost time & money. But how much time and money will you lose if the "not as deburred as one would like" conduit damages the insulation on your #8 conductors? It will cost even more if the fault shows up later and you have to come back to redo the entire job.
 

kwired

Electron manager
Location
NE Nebraska
If it's only 30 feet, why not dig it out and replace it with 1" PVC? Yes it's more work and will cost time & money. But how much time and money will you lose if the "not as deburred as one would like" conduit damages the insulation on your #8 conductors? It will cost even more if the fault shows up later and you have to come back to redo the entire job.
Maybe under a slab or something?
 