As suggested earlier, the next thing to do is beg, borrow, or steal a cl/amp probe to check around that conduit for an imbalance.
bikeindy said:. . . the travelers and switch legs are in one of the conduits . . . in conduit # 2 there are two 20 Amp circuits power feed and switch legs
How do you measure current in the conduit, without at the same time measuring the current in the wires contained by the conduit? The probe will see a magnetic field that is the sum of all fields created by all conductors that are within the clamp.tonyi said:One easy test should be to just clamp a probe on the pipe and see if its carrying any current.
boboelectric said:I had the same problem trying to switch mh fixtures on 3ways. Ended up using the 3ways to control a contactor.
Bob O.84,Pa.
bikeindy said:the lights are only pulling 17.5 Amps per switch.
the lights are only pulling 17.5 Amps per switch.