If you have 3 conductors in a conduit, using the heat dissipation assumptions of table 310.16 and 'back calculating' from 310.16, then #12 conductors carrying 17A should result in an insulation temperature of about 20C above ambient; a bit more than 100F in a 70F room.
The above is a very 'sketchy' calculation, since there is probably a considerable amount of rounding error in the table and the assumption about heat dissipation could be totally out to lunch. Additionally, I believe that the OP has more than 3 conductors in the conduit. In the original poster's installation, I would not be surprised by a temperature rise of anywhere from 10C to 40C depending upon conditions.
100F is quite warm (body temperature), but _not_ hot. Thus I am not content to simply say 'the wire is overloaded and it will get hot', even though I suspect that it is the problem. I believe that there is a real possibility of some other cause for this conduit heating.
If I understand the theory behind ampacity ratings, 17A on 12ga conductors is _not_ 'too much', even for a continuous load. It is probably too much for the breaker (most breakers are only listed for continuous operation at 80% of the trip level). It is also probably causing rapid wear on the switches, even if they are 20A switches.
-Jon
The above is a very 'sketchy' calculation, since there is probably a considerable amount of rounding error in the table and the assumption about heat dissipation could be totally out to lunch. Additionally, I believe that the OP has more than 3 conductors in the conduit. In the original poster's installation, I would not be surprised by a temperature rise of anywhere from 10C to 40C depending upon conditions.
100F is quite warm (body temperature), but _not_ hot. Thus I am not content to simply say 'the wire is overloaded and it will get hot', even though I suspect that it is the problem. I believe that there is a real possibility of some other cause for this conduit heating.
If I understand the theory behind ampacity ratings, 17A on 12ga conductors is _not_ 'too much', even for a continuous load. It is probably too much for the breaker (most breakers are only listed for continuous operation at 80% of the trip level). It is also probably causing rapid wear on the switches, even if they are 20A switches.
-Jon