tompoff43
Member
- Location
- Cincinnati
- Occupation
- Electrical designer
I have a project they are wanting to mount the conduit to the fence.. Per NEC can exterior conduit pvc or rigid steel be supported by a fence structural alone?
Chain link.What sort of fence?
Short answer looks like No.358.30 Securing and Supporting. EMT shall be installed as a
complete system in accordance with 300.18 and shall be
securely fastened in place and supported in accordance with
358.30(A) and (B).
(A) Securely Fastened. EMT shall be securely fastened in
place at intervals not to exceed 3 m (10 ft). In addition, each
EMT run between termination points shall be securely fastened
within 900 mm (3 ft) of each outlet box, junction box, device
box, cabinet, conduit body, or other tubing termination.
Exception No. 1: Fastening of unbroken lengths shall be permitted to be
increased to a distance of 1.5 m (5 ft) where structural members do not
readily permit fastening within 900 mm (3 ft).
N
FOR INDIVIDUAL Copyright 2022 National Fire Protection Association (NFPA®). Licensed by agreement to Michael Olson FOR INDIVIDUAL USE ONLY and downloaded on 08/04/2022. No reproduction or transmission in any form permitted without
written permission of NFPA®. For inquiries or access for multiple users, or to report unauthorized use, contact orders@nfpa.org.
{D9DA063F-016D-4ABB-A149-71CEDDE382F4}
ARTICLE 360 — FLEXIBLE METALLIC TUBING: TYPE FMT 360.56
2017 Edition NATIONAL ELECTRICAL CODE 70 –211
Exception No. 2: For concealed work in finished buildings or prefinished
wall panels where such securing is impracticable, unbroken
lengths (without coupling) of EMT shall be permitted to be fished.
(B) Supports. Horizontal runs of EMT supported by openings
through framing members at intervals not greater than 3 m
(10 ft) and securely fastened within 900 mm (3 ft) of termination
points shall be permitted.
Is it Secure ? ... Chain Link kind of flimsy.
Why not?
JAP>
Not that it changes anything but you weren't asking about EMT and I agree with JAPs response FWIWShort answer looks like No.
IMO ... It doesn't look professional.
I agree, it's a judgment call ... But, your work is a symbol of your product for all to see.
Some people only need and want a KIA others want to spend money and want a CadillacI think this is a good time to discuss workmanship:
1. Install the job the cheapest way possible and to code.
2. Install the job in a professional and workmanlike manner.