tompoff43

Member
Location
Cincinnati
Occupation
Electrical designer
I have a project they are wanting to mount the conduit to the fence.. Per NEC can exterior conduit pvc or rigid steel be supported by a fence structural alone?
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
358.30 Securing and Supporting. EMT shall be installed as a
complete system in accordance with 300.18 and shall be
securely fastened in place and supported in accordance with
358.30(A) and (B).
(A) Securely Fastened. EMT shall be securely fastened in
place
at intervals not to exceed 3 m (10 ft). In addition, each
EMT run between termination points shall be securely fastened
within 900 mm (3 ft) of each outlet box, junction box, device
box, cabinet, conduit body, or other tubing termination.
Exception No. 1: Fastening of unbroken lengths shall be permitted to be
increased to a distance of 1.5 m (5 ft) where structural members do not
readily permit fastening within 900 mm (3 ft).
N
FOR INDIVIDUAL Copyright 2022 National Fire Protection Association (NFPA®). Licensed by agreement to Michael Olson FOR INDIVIDUAL USE ONLY and downloaded on 08/04/2022. No reproduction or transmission in any form permitted without
written permission of NFPA®. For inquiries or access for multiple users, or to report unauthorized use, contact orders@nfpa.org.
{D9DA063F-016D-4ABB-A149-71CEDDE382F4}
ARTICLE 360 — FLEXIBLE METALLIC TUBING: TYPE FMT 360.56
2017 Edition NATIONAL ELECTRICAL CODE 70 –211
Exception No. 2: For concealed work in finished buildings or prefinished
wall panels where such securing is impracticable, unbroken
lengths (without coupling) of EMT shall be permitted to be fished.
(B) Supports. Horizontal runs of EMT supported by openings
through framing members at intervals not greater than 3 m
(10 ft) and securely fastened within 900 mm (3 ft) of termination
points shall be permitted.


Is it Secure ? ... Chain Link kind of flimsy.
 
Last edited:

tompoff43

Member
Location
Cincinnati
Occupation
Electrical designer
358.30 Securing and Supporting. EMT shall be installed as a
complete system in accordance with 300.18 and shall be
securely fastened in place and supported in accordance with
358.30(A) and (B).
(A) Securely Fastened. EMT shall be securely fastened in
place
at intervals not to exceed 3 m (10 ft). In addition, each
EMT run between termination points shall be securely fastened
within 900 mm (3 ft) of each outlet box, junction box, device
box, cabinet, conduit body, or other tubing termination.
Exception No. 1: Fastening of unbroken lengths shall be permitted to be
increased to a distance of 1.5 m (5 ft) where structural members do not
readily permit fastening within 900 mm (3 ft).
N
FOR INDIVIDUAL Copyright 2022 National Fire Protection Association (NFPA®). Licensed by agreement to Michael Olson FOR INDIVIDUAL USE ONLY and downloaded on 08/04/2022. No reproduction or transmission in any form permitted without
written permission of NFPA®. For inquiries or access for multiple users, or to report unauthorized use, contact orders@nfpa.org.
{D9DA063F-016D-4ABB-A149-71CEDDE382F4}
ARTICLE 360 — FLEXIBLE METALLIC TUBING: TYPE FMT 360.56
2017 Edition NATIONAL ELECTRICAL CODE 70 –211
Exception No. 2: For concealed work in finished buildings or prefinished
wall panels where such securing is impracticable, unbroken
lengths (without coupling) of EMT shall be permitted to be fished.
(B) Supports. Horizontal runs of EMT supported by openings
through framing members at intervals not greater than 3 m
(10 ft) and securely fastened within 900 mm (3 ft) of termination
points shall be permitted.


Is it Secure ? ... Chain Link kind of flimsy.
Short answer looks like No.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
I agree, it's a judgment call ... But, your work is a symbol of your product for all to see.

For me, strapping conduit to a cyclone fence isn't it.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
If the fence has a rigid frame along the top, I have bolted Minerallac straps back to back and used that as support in the past. I agree that it doesn't look as nice as using PVC underground and emerging from grade where the conduit terminates.
 

jap

Senior Member
Occupation
Electrician
Point is, there are many different types of fences.

Wood, metal, plastic, silt, tall, short, fancy, dilapidated, solid, perforated, etc....

As far as running conduit on it, if it meets the requirements for support and fastening there is no reason it cant be used.

To speculate on a hard, yes, no, green tag or red tag would be impossible without actually seeing the fence in question, and, how the conduit was actually ran on it.

JAP>
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
I think this is a good time to discuss workmanship:
1. Install the job the cheapest way possible and to code.
2. Install the job in a professional and workmanlike manner.
 

jap

Senior Member
Occupation
Electrician
I agree.

I've seen beautiful fences destroyed by crappy pipe runs.
I've seen beautiful pipe runs installed on crappy fences.
I've seen beautiful pipe runs installed on beautiful fences.

It seems the code allows pipe runs to be installed on fences.

JAP>
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think this is a good time to discuss workmanship:
1. Install the job the cheapest way possible and to code.
2. Install the job in a professional and workmanlike manner.
Some people only need and want a KIA others want to spend money and want a Cadillac
 