Yes, the conduit runs in the V-groove, and the wall stops at the roof deck.Are you talking about the trapezoidal shape in a corrugated deck? #1 where does the rated assembly stop is there to be a rated ceiling? #2 08' NEC if that is the roof deck then that could be a problem 300.4(E)....I am just assuming here.
Yes, the conduit runs in the V-groove, and the wall stops at the roof deck.
Is that metal ceiling the roof deck ?? He might have a 300.4(E) issue if it is