CONDUIT SUPPORTS

Status
Not open for further replies.

winslowfam

Senior Member
Location
VA
Hi...we are designing conduit system with supports and have a quick question. Code says to support conduit every 10' min. or use spacing based on table. We have a couple of 2" rigid conduits and a couple of smaller 3/4" conduits. The table allows supports every 16' for 2". Can I support 3/4" conduit off of 2" conduits during span to keep structural support spacing at 16'? Does the code allow that?
 
Re: CONDUIT SUPPORTS

Thanks...is that called out somewhere in the code? It was my general feel, too, since rigid is threaded.
 
Re: CONDUIT SUPPORTS

Originally posted by winslowfam:
Thanks...is that called out somewhere in the code? It was my general feel, too, since rigid is threaded.
article 358 describes emt, its allowed uses, and dissallowed uses. i believe you will find a prohibition on hanging anything from emt except fittings in that article.

the articles describing rmc and imc do not contain that prohibition.

if it is not prohibited, it is allowed.
 