stickboy1375
Senior Member
- Location
- Litchfield, CT
220/221 said:Eh...I'm goin with, the inside of the conduit is normally dry.
Whatever... :roll:
220/221 said:Eh...I'm goin with, the inside of the conduit is normally dry.
220/221 said:Eh...I'm goin with, the inside of the conduit is normally dry.
jamesguy10 said:Ive never done this, but then again we dont have any residential RTU's here
Quote:
It is intended that the inside of a raceway in a wet location or a raceway installed underground be considered a wet location. Therefore, any conductors contained therein would be required to be suitable for wet locations.
stew said:Just as an additional comment if you are going to use emt as a sleeve you must bond it.
JohnJ0906 said:Where is this commentary located in the '05 NECHB?
stew said:Just as an additional comment if you are going to use emt as a sleeve you must bond it.
wbalsam1 said:Look at the raceway Article. For example try Art. 348 Type FMC and read the commentary at 348.12 :smile:
Quote:
It is intended that the inside of a raceway in a wet location or a raceway installed underground be considered a wet location. Therefore, any conductors contained therein would be required to be suitable for wet locations.
Nevermind that... see the new 300.5(B) in 2008.JohnJ0906 said:Where is this commentary located in the '05 NECHB?
stew said:short sections of metal raceway is in 250.132 as pointed out by my favorite electrical inspector when i forgot.