Hope I can do this justice. Have a pull box in the ceiling of an office building. One of the conduits comes into the box at about a 22 degree angle (maybe a little less) so that only about one tooth of the lock nut is even touching the box (no grounding conductor). The contractor wants to tell me that it's to code so I open the box, which I hadn't done previously (that's when I saw the lock nut) and there were two four inch holes in the back of the box and no plastic bushings on the conduit.
Still want to argue code?