So you guys are saying that balanced loads or Net Zero loads will not create any heating of conductors.
That using too small a conductor , too many conductors in a conduit, or the ballasts of these grow light privide no contribution to heating of the conduit.
Nope, what I am saying is that I don't understand how you don't end up with a net 0 magnetic field if the conductors in the conduit end up with a net 0 current. In particular when you wrap a clamp meter or window CT around all the wires and read 0 amps, that tells me that the magnetic field is 0.
Thermally, it is entirely different, the watt losses in each conductor sum no matter the vector direction.