David I have seen many units like this. They are all lower than what the nec allows.... I think the efficiency of the units has gotten so good that they don't think it needs a high overcurrent protective device.
Seriously take a look at the new units. Everyone I have seen has had a max just above the min cir ampacity
The efficiency of the units doesn't change the MCA requirements. The unit doesn't give and MCA value as per Code requirements.
If the compressor RLA is 18.25A, the unit MCA can't be 19.8A per NEC requirements.