Keep in mind the NEC does not require HVAC equipment to be
'listed' other local mechanical codes probably do though.
The NEC is for when YOU have to determine MCA and MOCP in the field from basic nameplate information. For an EQUIPMENT MANUFACTURER, they need to satisfy UL standards, in this case probably UL1995, which has its own set of rules for determining the motor amp loading based on what the equipment mfr expects in terms of performance, then that is used in their MCA and MOCP data. So once THEY provide you with the MCA and MOCP, you need only follow those values, you do not calculate them again.
David's right that Equipment Manufacturers still need to follow the rules in Art 440 for an AHJ (in a NEC jurisdiction) to accept their products.
See 110.2,
Just like any other case when the NEC does not require listing manufactures need to follow the NEC labeling rules.
The NEC says the equipment shall be marked with the minimum supply circuit conductor ampacity, as determined by Part IV of Article 440 of the NEC.
You are correct that 440.4(B) Requires the manufacturer to mark the
'minimum supply circuit conductor ampacity'
And 440.4(C) Deals with branch circuit selection current.
My question to David is are you saying 440.22 is dictating minimums for the manufacturer to calculate this?
They way I read 440.22 is those are maximum's the manufactures
'minimum supply circuit conductor ampacity' calc cannot exceed.
As per 90.1(B) the NEC wont get involved with this minimum calculation, rather the maximum values that can be considered 'necessary for safety'
Keep in mind UL 1995 4.5 specified the printed instructions are infact included in the listing so 110.3(B) applies.
UL 1995 44.14 states how to calculate the 'minimum circuit ampacity' :