690.64 Point of Connection. The output of a utilityinteractive
inverter shall be connected as specified in
690.64(A) or (B).
(A) Supply Side. The output of a utility-interactive inverter
shall be permitted to be connected to the supply side
of the service disconnecting means as permitted in
230.82(6).
(B) Load Side. The output of a utility-interactive inverter
shall be permitted to be connected to the load side of the
service disconnecting means of the other source(s) at any
distribution equipment on the premises. Where distribution
equipment, including switchboards and panelboards, is fed
simultaneously by a primary source(s) of electricity and
one or more utility-interactive inverters, and where this distribution
equipment is capable of supplying multiple branch
circuits or feeders, or both, the interconnecting provisions
for the utility-interactive inverter(s) shall comply with
(B)(1) through (B)(7).
(1) Dedicated Overcurrent and Disconnect. Each source
interconnection shall be made at a dedicated circuit breaker
or fusible disconnecting means.
(2) Bus or Conductor Rating. The sum of the ampere
ratings of overcurrent devices in circuits supplying power
to a busbar or conductor shall not exceed 120 percent of the
rating of the busbar or conductor. In systems with panelboards
connected in series, the rating of the first overcurrent
device directly connected to the output of a utilityinteractive
inverter(s) shall be used in the calculations for
all busbars and conductors.
(3) Ground-Fault Protection. The interconnection point
shall be on the line side of all ground-fault protection
equipment.
Exception: Connection shall be permitted to be made to
the load side of ground-fault protection, provided that there
is ground-fault protection for equipment from all groundfault
current sources. Ground-fault protection devices used
with supplies connected to the load-side terminals shall be
identified and listed as suitable for backfeeding.
(4) Marking. Equipment containing overcurrent devices in
circuits supplying power to a busbar or conductor supplied
from multiple sources shall be marked to indicate the presence
of all sources.
(5) Suitable for Backfeed. Circuit breakers, if backfed,
shall be suitable for such operation.
FPN: Circuit breakers that are marked ?Line? and ?Load?
have been evaluated only in the direction marked. Circuit
breakers without ?Line? and ?Load? have been evaluated in
both directions.
(6) Fastening. Listed plug-in-type circuit breakers backfed
from utility-interactive inverters complying with 690.60
shall be permitted to omit the additional fastener normally
required by 408.36(D) for such applications.
(7) Inverter Output Connection. Unless the panelboard
is rated not less than the sum of the ampere ratings of all
overcurrent devices supplying it, a connection in a panelboard
shall be positioned at the opposite (load) end from
the input feeder location or main circuit location. The bus
or conductor rating shall be sized for the loads connected in
accordance with Article 220. A permanent warning label
shall be applied to the distribution equipment with the following
or equivalent marking:
WARNING
INVERTER OUTPUT CONNECTION
DO NOT RELOCATE
THIS OVERCURRENT DEVICE